EWS server - it takes ~30 seconds until ValueItem's value is updated in the EBO's Watch pane
SmartConnector Forum
Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2020-11-0211:07 AM
Hi Michael,
By default, EBO only polls for updated values from an EWS server every 60 seconds.
Please take a look at the properties of the EWS Interface in EBO and see what the value in "Value Poll Internal (s)" is. Feel free to reduce this down to something lower.
Link copied. Please paste this link to share this article on your social media post.
2020-11-0211:07 AM
Hi Michael,
By default, EBO only polls for updated values from an EWS server every 60 seconds.
Please take a look at the properties of the EWS Interface in EBO and see what the value in "Value Poll Internal (s)" is. Feel free to reduce this down to something lower.