Alarm Push processor - can we get the alarm's Description?

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • Alarm Push processor - can we get the alarm's Description?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Start a Topic
Solved
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-09-12 10:19 AM

0 Likes
14
3344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-12 10:19 AM

Alarm Push processor - can we get the alarm's Description?

Hi,

 

We have a SmartConnector Push processor that receives alarms in real-time from the EBO. The question is:

 

Can this processor receive the alarm's Discovery property from the EBO? 

 

See the attached screen capture of the class we are suing.

 

Thank you.

 

Mike

 

 

 

 

Attachments
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-10-01 01:24 AM

0 Likes
1
3302
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-01 01:24 AM

Hi Armend,

 

Thank you. I shall mark this as a solution. Can you add the "Note 1" and "Note 2" to the EWS in the future?

 

Thanks.

 

Michael

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 14
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-09-13 01:07 AM

0 Likes
13
3335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-13 01:07 AM

Hi,

 

From what I understand from your screenshot, you are using the AlarmItemReader, which in turn uses the GetAlarmEvents and GetUpdatedAlarmEvents EWS endpoints. These get the AlarmEvents, and not the AlarmItems. If you are looking for the alarms Description property, you'll have to make an additional call(GetItems), fetching the AlarmItem, to get the property. 

 

BR

Armend

 

 

Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-09-28 09:29 AM

0 Likes
12
3331
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-28 09:29 AM

Hi Armend,

 

Thank you for your answer. Can we also get the alarm's 'Note 1' and 'Note 2' using the GetItems API?

 

Thank you.

 

Mike

 

 

Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-09-28 11:03 AM

0 Likes
11
3328
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-28 11:03 AM

Hi Armend,

 

I am trying the Swagger in SmartConnector to get the alarm's Description, Note 1 and Note 2.

I have the following alarm ID:

02-Server 1-MyValues-Building-10thTemp Out of Range Alarm

 

After URL Encode it is:

02-Server%201-MyValues-Building-10thTemp%20Out%20of%20Range%20Alarm

 

Can you point me to the right API in the Swagger?

 

Thanks.

 

Mike

Attachments
Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-09-28 09:48 PM

0 Likes
10
3326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-28 09:48 PM

Hi,

 

It's GET /Values/{Id}/Description

 

You cannot get Notes as it is not part of EWS.

 

BR

Armend

Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-09-28 10:02 PM

0 Likes
9
3324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-28 10:02 PM

Hi Armend,

 

Thank you for your answer. 

 

I have tried it and got an error 404. Please see the attached file.

 

Any idea what is the problem?

 

The alarm ID is: 02-Server 1-MyValues-Building-10thTemp Out of Range Alarm

After URL Encode it is: 02-Server%201-MyValues-Building-10thTemp%20Out%20of%20Range%20Alarm

 

Thank you.

 

Mike

 

 

Attachments
Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-09-28 10:52 PM

0 Likes
8
3322
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-28 10:52 PM

If the EWS server is an EBO system, your ID looks wrong. 

 

It should be in this format: 

 

02/Server 1/Example Objects/Test Alarm

Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-09-30 05:42 AM

0 Likes
7
3317
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-30 05:42 AM

Hi Armend,

 

Thank you for your answer. Can our discovery processor get the Alarm Description, Note 1 and Note 2?

Currently our alarm discovery processor discovers these properties:

Alarm-ID

Alarm Presentation (Message) - Above Upper limit message / Below lower limit message

Above Upper limit Priority

Below Upper limit Priority

 

Thank you.

 

Mike

 

Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-09-30 07:57 AM

0 Likes
6
3315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-30 07:57 AM

I don't think you can get the Notes through EWS.

 

You can get the Description with your processor using the EWS client.

Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-09-30 08:15 AM

0 Likes
5
3314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-30 08:15 AM

Hi Armend,

 

Thank you for your answer. I didn't see any API to retrieve the Above Upper limit Priority and Below Upper limit Priority but our processor is able to retrieve (using the source I sent you).

 

Similarly, can we retrieve the other fields during the discovery? (Notes and Description)

 

Thanks.

 

Mike

 

 

Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-09-30 08:25 AM

0 Likes
4
3312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-30 08:25 AM

I believe Notes cannot be retrieved. Description can be fetched with GetItems, not with GetValues, which the chunk of code you sent me is using. 

Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-09-30 08:53 AM

0 Likes
3
3310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-30 08:53 AM

Hi Armend,

 

Thank you for your answer. Can you please point me to the documentation of the GetValuesItems API?

 

Thanks.

 

Mike

Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-10-01 12:16 AM

0 Likes
2
3307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-01 12:16 AM

This is the EWS spec. This is what the Smartconnector client uses and the GetValues request is in there too.

Attachments
Tags (1)
  • Tags:
  • english
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-10-01 01:24 AM

0 Likes
1
3303
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-01 01:24 AM

Hi Armend,

 

Thank you. I shall mark this as a solution. Can you add the "Note 1" and "Note 2" to the EWS in the future?

 

Thanks.

 

Michael

Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-10-01 01:29 AM

0 Likes
0
3298
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-01 01:29 AM

This is unfortunately not in my control, but I'll talk to the dev team behind EWS to see if it's possible.

 

BR

Armend

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore