Wiser OpenTherm Setting the Flow Temp on Combi Viessmann

Schneider Electric Wiser Forum

Connect with Wiser Smart Home solution experts in the Schneider Electric Wiser forum. Discuss tips on features, updates, installation, and how to get the most out of your Wiser products.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Schneider Electric Wiser
  • Schneider Electric Wiser Forum
  • Wiser OpenTherm Setting the Flow Temp on Combi Viessmann
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
David_SE
Captain David_SE Captain
149
Alfred_SE
Alfred_SE Schneider Alumni (Retired)
24
Maude.wiser.
Lieutenant Maude.wiser. Lieutenant
22
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Schneider Electric Wiser Forum
Start a Topic
Solved
hanwellr
hanwellr
Cadet

Posted: ‎2024-09-18 03:27 AM

0 Likes
5
2533
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-18 03:27 AM

Wiser OpenTherm Setting the Flow Temp on Combi Viessmann

Hello,

I have Wiser kit 1 working with Openthem  on a Viessmann Combi. There are no issues and the Combi is set up to take Openthem commands. 

 

The question is should I alter the maximum flow tempurature from 80 to 60? What i'm wondering is if the Openthem does alter the requested flow temp. Seem each time I ask for a room to be heated the request is going for 100% (80) and never see a request lower? My understanding is that as the room gets to temp then the request should be lower than 100% and there for the flow should be lower?

 

Wonder if other people just set a lower flow temp at the boiler to get around this. 

Labels
  • Labels:
  • About Wiser
  • Temperature Control
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Crankyman
Crewman Crankyman
Crewman

Posted: ‎2024-09-30 11:53 AM

0 Likes
4
2450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-30 11:53 AM

I have a Viessmann combi with a kit 1 too.

My flow temp does drop from the initial 80 as the room temperature starts to climb and I've seen flow temps of 35.  I find the initial flow rate of 80 very annoying as I don't believe it's necessary, and a lower flow temp would be more appropriate as radiators at 80 are very hot!

I've tried to lower the maximum flow temperature on the boiler, but as per the opentherm spec, the controller (Wiser HubR) commands the temperature and overrides any changes on the boiler, so I don't think you can lower the flow temp whilst wired for opentherm.

 

My system works well overall, but I really do hate that initial 10 minutes or so at 80 degrees before the temperature throttles back.

 

I'm toying with fitting the external temperature sensor and letting the Viessmann control the flow temp according to how cold it is outside (Temperature compensation) and just use the Wiser system to call the heating on and off so it's not running 24/7.  However I'm not sure whether the system would need to run longer at lower flow temperatures, rather than me turning the boiler on and off  using the Wiser system.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Crankyman
Crewman Crankyman
Crewman

Posted: ‎2024-09-30 11:53 AM

0 Likes
4
2451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-30 11:53 AM

I have a Viessmann combi with a kit 1 too.

My flow temp does drop from the initial 80 as the room temperature starts to climb and I've seen flow temps of 35.  I find the initial flow rate of 80 very annoying as I don't believe it's necessary, and a lower flow temp would be more appropriate as radiators at 80 are very hot!

I've tried to lower the maximum flow temperature on the boiler, but as per the opentherm spec, the controller (Wiser HubR) commands the temperature and overrides any changes on the boiler, so I don't think you can lower the flow temp whilst wired for opentherm.

 

My system works well overall, but I really do hate that initial 10 minutes or so at 80 degrees before the temperature throttles back.

 

I'm toying with fitting the external temperature sensor and letting the Viessmann control the flow temp according to how cold it is outside (Temperature compensation) and just use the Wiser system to call the heating on and off so it's not running 24/7.  However I'm not sure whether the system would need to run longer at lower flow temperatures, rather than me turning the boiler on and off  using the Wiser system.

Reply

Link copied. Please paste this link to share this article on your social media post.

heinzbean
heinzbean
Cadet

Posted: ‎2024-12-07 07:14 AM

In response to Crankyman
0 Likes
3
2251
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-07 07:14 AM

Crankyman

I read that Opentherm takes care of the flow temps. I manually set my flow temp on the boiler to 55 degrees.

Also i was going to fit an external temp compensation sensor . but realised the Wiser App already has this included. The Opentherm works super efficient for me ...The boiler is nearly always  in eco-mode .House nice an warm and gas bill Half it was previously....

Reply

Link copied. Please paste this link to share this article on your social media post.

Crankyman
Crewman Crankyman
Crewman

Posted: ‎2024-12-11 04:45 PM

In response to heinzbean
0 Likes
2
2226
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-11 04:45 PM

Hi Heinzbean,

Opentherm should take care of the flow temperature, so you shouldn't be able to manually set your flow temp to 55?  I certainly can't on mine, if I select the radiator temp on the boiler control panel it won't let me adjust anything, I can of course set the hot water temp Ok. Is your boiler hard wired for opentherm or just how you've set it in the app?

My issue is similar to Hanwellr, that initial turn on when the flow temp spikes to 80, presumably to warm the house up quickly, but I find the hot radiators overpowering, and I don't think it's necessary most of the time as it's rarely below freezing in the UK. After a while the flow temp starts to come down and as you say it then runs nicely in eco-mode.

The wiser app doesn't work in the same way for weather compensation, (I should've said weather and not temperature compensation in my previous post), if you add an external sensor to the boiler it will control the flow temp according to the outside temperature and not necessarily take in to consideration any internal temperature settings.  I believe it's supposed to be very efficient and economical, it's not a straight line from boiler off at say 20 outside to 55 at 5 outside but a curve programmed into the boiler, of which there are several you can choose from to get a comfortable inside temp, at least that's my understanding from the boiler manual. This Viessmann brochure explains it much better than I can

I keep threatening to buy the sensor and try it, but I haven't done yet!

 

Reply

Link copied. Please paste this link to share this article on your social media post.

hanwellr
hanwellr
Cadet

Posted: ‎2024-12-13 02:57 AM

In response to Crankyman
0 Likes
0
2210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-13 02:57 AM

Thanks for the update yes geting simlar feed back from the app. One thing I did notice in Home assistant I have the wiser feeding back and notice there is no value for the return temp. 

 

What I have done outside of this is build ESP32 temp sensor and have one on the flow and return pipe. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Lactophobe
Crewman Lactophobe
Crewman

Posted: ‎2025-04-24 07:10 AM

In response to Crankyman
0 Likes
0
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-24 07:10 AM

From Viessmann...

Weather compensation or Open therm can only be used individually it would only be a case of using one or the other 

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore