Under Range and Over Range SCADAPack x70 independent of RAW and ENG values

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • Under Range and Over Range SCADAPack x70 independent of RAW and ENG values
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Remote Operations Forum
Start a Topic
Solved
AlbertoArdila
Lieutenant AlbertoArdila
Lieutenant

Posted: ‎2022-01-17 05:37 AM

0 Likes
2
1694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-17 05:37 AM

Under Range and Over Range SCADAPack x70 independent of RAW and ENG values

Hi

In Workbech there are the function RDFLD_I  (reads an point attribute or property and returns the value in a 32 bit integer variable). That function is used to get the Over Range and Under Range of an Analog input.

I want to know if in SCADAPack x70 Logic there is an equivalent.

In SCADAPack x70 Logic, I know that I can configure le Under and Over range in the Object input attributes but their limits are dependent on the Eng. Values.

I want that the under an over range are actives by the current (4 -20 mA values) example: 3.9 mA = Under Range and 4.1mA = Over Range and independents of the Raw and Eng. Configured values.

Thank you.

Labels
  • Labels:
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2022-01-17 09:02 AM . Last Modified: ‎2022-01-17 09:44 AM

0 Likes
1
1686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-17 09:02 AM . Last Modified: ‎2022-01-17 09:44 AM

Hello Alberto,

 

Each x70 analog input may be configured as 0-20 or 4-20 mA easily. On the configuration tab, select Physical I/O then Local. Select the SCADAPack, then in the Channel Configuration column scroll down to the desired analog input. The type column is at the far-right. If using a smaller screen like a laptop that column might be hidden off to the right. See the attached image.

 

In RemoteConnect you may configure as many as four "Low" and four "High" levels (on the Alert Notifications tab) for each analog object. The values are assigned by you - they are not locked at (eg) 4.0 and 20.0 mA. 

 

In your logic you may use any or all of these as required. Also, these level values may easily be changed in logic at any time. Creating an object with a Logic Variable Type of T_SPx70_ADV_ANALOG provides access to these and many other attributes of the analog object.

 

Joel Weder
Remote Operations Specialist
Schneider Electric

See Answer In Context

Attachments
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2022-01-17 09:02 AM . Last Modified: ‎2022-01-17 09:44 AM

0 Likes
1
1687
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-17 09:02 AM . Last Modified: ‎2022-01-17 09:44 AM

Hello Alberto,

 

Each x70 analog input may be configured as 0-20 or 4-20 mA easily. On the configuration tab, select Physical I/O then Local. Select the SCADAPack, then in the Channel Configuration column scroll down to the desired analog input. The type column is at the far-right. If using a smaller screen like a laptop that column might be hidden off to the right. See the attached image.

 

In RemoteConnect you may configure as many as four "Low" and four "High" levels (on the Alert Notifications tab) for each analog object. The values are assigned by you - they are not locked at (eg) 4.0 and 20.0 mA. 

 

In your logic you may use any or all of these as required. Also, these level values may easily be changed in logic at any time. Creating an object with a Logic Variable Type of T_SPx70_ADV_ANALOG provides access to these and many other attributes of the analog object.

 

Joel Weder
Remote Operations Specialist
Schneider Electric
Attachments
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

AlbertoArdila
Lieutenant AlbertoArdila
Lieutenant

Posted: ‎2022-01-20 06:43 AM

In response to Joel_Weder
0 Likes
0
1677
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-20 06:43 AM

Hi Joel Weder

 

Thanks for the reply

 

I go to use the Analog Input object properties for Over and Under Range Limit.

 

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore