Trio E/M and Q Radios.

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • Trio E/M and Q Radios.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Remote Operations Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2020-08-24 10:39 AM

0 Likes
3
3939
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-24 10:39 AM

Trio E/M and Q Radios.

current configuration is as follow.

Base Station Radio is E-series Er450 and Remote side radio is M-series.

Now i have a requirement to use the Port-B of E-series because i have an additional system other then the existing Scada System.

As M-series radio has only 1 port so i have to change the radio at remote site which have 2 ports. so i selected Q series Radios which have 2 ports. Now there are 2 different masters connected to each port of E- series Radio polling their respective slaves at each remote sites connected to each port of Q series radios. But i am facing data loss on one of the port.

I have tried Collision Avoidance techniques still i am facing data loss on one of the port.

 

I am looking to the solution how could i manage to minimize the loss of data.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2020-08-24 01:53 PM

In response to Anonymous user
0 Likes
0
3924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-24 01:53 PM

Hello @Anonymous user 

 

I have sent a note to our Tech Support team asking for them to reach out to you. Hopefully tomorrow morning they can do so.

 

One item that stands out in the list of configuration items you mentioned is the Maximum Packet Size. The packet size of 2500 is VERY LARGE, and could cause problems. Sending a packet this size at a radio data rate of 9600 bps would take almost 3 seconds. It is quite possible that a burst of noise or interference could cause the message to be lost.

 

While it might be possible to configure the Maximum Frame size to 2000 bytes, it is certainly not advisable. These messages would be much more likely to succeed if they were perhaps somewhere in the range of 200-500 bytes or so. 

 

After you have made that change, I suggest you test the communication again. If still not working, SAVE configuration files for the Master radio and the remote radios that are experiencing the problem, and send them to the Tech Support address given earlier. Also, in the same email please describe your Custom protocol as clearly as you can. It is a bit unusual for a serial SCADA protocol to send messages that 2000 bytes long.

 

Joel Weder
Remote Operations Specialist
Schneider Electric

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2020-08-24 12:41 PM . Last Modified: ‎2020-08-24 12:48 PM

0 Likes
2
3935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-24 12:41 PM . Last Modified: ‎2020-08-24 12:48 PM

Hello  @Anonymous user,

 

 First, I should say that if you are looking for help getting your radios working right away, this is really not the best place to ask your questions. Instead you can contact our Technical Support team:
SupportTRSS@se.com or
1-888-226-6876

 

I can respond generally though. Certainly, the Trio QR450 radio can replace Trio ER450 (two serial ports) or ER45e (one serial, one ethernet) radios, when configured for the E/M Compatibility mode. As you're trying to set up two serial ports you would need to configure both serial ports of the radio, after it's been changed to E/M Compatibility mode.

 

You must ensure that the Port stream ID's match at both ends of the link, and that they are different between the two ports. For example, Port A could use SID 3 for both Rx and Tx, and Port B can use SID 5 for both Rx and Tx.

 

If you use different SID's for Rx and Tx, they must be reversed at the distant radios. Different Rx/Tx SID's is not necessary except for unusual cases, but if you are doing that, typically it would be something like:

 

Port A      Master Radio: Rx = 3, Tx = 4     Remote radios: Rx = 4, Tx = 3

Port B      Master Radio: Rx = 5, Tx = 6     Remote radios: Rx = 6, Tx = 5

 

Typically Carrier Detect collision avoidance mode does a pretty good job to minimize collisions. Ensure that is enabled in all radios. Also, the E Series radios (or Q series acting as E Series) has a transmit data buffer for each serial port, and will only allow one port to access the radio channel at a time. However, if two remote device at different sites both decide to transmit at the same time there is not much that Carrier Detect collision avoidance can do about that. (especially if those two sites cannot hear each other)

 

Also, of course, the serial port settings must match in the radio and devices connected to each port of the radio. And the serial cables should be standard 3-wire straight-through type.

 

Again, I do suggest you contact our Tech Support team for any further assistance with this issue.

 

Joel Weder
Remote Operations Specialist
Schneider Electric
  • Tags:
  • english
  • wireless
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-08-24 01:22 PM

In response to Joel_Weder
0 Likes
1
3931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-24 01:22 PM

Dear @Joel_Weder ,

 

First I would like to thank you for your generous reply.

 

Secondly I was in contact with the support guy regarding this issue but from last couple of week I didn't hear from him despite sending reminder again and again that's y I came to this platform.

 

My current settings are as below.

 

Base station radio is ER450.

Both ports enabled port A is standard modbus port.

Port b is customized as per our requirements.

Character layer is custom settings 38400, N, 8,1

Packet layer is custom settings maximum bytes 2500, minimum bytes 11.

 

SIDs are different for TX and RX same as mentioned you.

 

Remote site radios are Q series configured as E modulation with above same port configurations.

 

Collision avoidance applied as carrier detector at both ends.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Joel_Weder
Captain Joel_Weder Captain
Captain

Posted: ‎2020-08-24 01:53 PM

In response to Anonymous user
0 Likes
0
3925
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-24 01:53 PM

Hello @Anonymous user 

 

I have sent a note to our Tech Support team asking for them to reach out to you. Hopefully tomorrow morning they can do so.

 

One item that stands out in the list of configuration items you mentioned is the Maximum Packet Size. The packet size of 2500 is VERY LARGE, and could cause problems. Sending a packet this size at a radio data rate of 9600 bps would take almost 3 seconds. It is quite possible that a burst of noise or interference could cause the message to be lost.

 

While it might be possible to configure the Maximum Frame size to 2000 bytes, it is certainly not advisable. These messages would be much more likely to succeed if they were perhaps somewhere in the range of 200-500 bytes or so. 

 

After you have made that change, I suggest you test the communication again. If still not working, SAVE configuration files for the Master radio and the remote radios that are experiencing the problem, and send them to the Tech Support address given earlier. Also, in the same email please describe your Custom protocol as clearly as you can. It is a bit unusual for a serial SCADA protocol to send messages that 2000 bytes long.

 

Joel Weder
Remote Operations Specialist
Schneider Electric
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore