RemoteConnect Poll Offset

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • RemoteConnect Poll Offset
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Remote Operations Forum
Start a Topic
fcantrell
Ensign fcantrell
Ensign

Posted: ‎2020-06-30 08:17 AM

0 Likes
4
2959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-30 08:17 AM

RemoteConnect Poll Offset

Is there a way to leave quiet time between Master polls to remote devices in RemoteConnect? Looking for a setting similar to the "Poll Offset" setting in Telepace.

Labels
  • Labels:
  • DNP3
  • SCADA
  • Telemetry
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-07-01 04:28 AM

0 Likes
3
2952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-01 04:28 AM

This is when using the SCADAPack x70 as a DNP3 Master / Data Concentrator right?

 

I can't see this exact setting in the Data Concentrator options for RemoteConnect, but you could 'emulate' the same thing using some logic.

 

If you go to the Data Concentrator Master section, and under the selected device you want to time the polls for, under the 'Status and Control Configuration' you can assign an Object Association to the 'Force Event Poll', and the 'Force Integrity Poll' (and others you care to do.. like Force Warm Restart etc).

Then from within your logic you could do the polling of the slave devices however you'd like.

 

Obviously not as 'set and forget' as the Poll Offset control you mention, but it's still possible.

If I were you, I'd probably get in touch with your local rep to raise a feature request ticket for an identical setting to the 'Poll Offset' if this is something that you will need to be doing often.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

fcantrell
Ensign fcantrell
Ensign

Posted: ‎2020-07-01 02:16 PM

In response to BevanWeiss
0 Likes
2
2947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-01 02:16 PM

Thanks for the reply. Yes, this would indeed be used in DNP3 Master/ Data Concentrator mode. This is a very useful feature in the Telepace DNP3 Master configuration. It allows dead time between master polls so unsolicited messages can get through. Without this setting, the master will poll all the remote sites one after another until all polls are done. If you have a lot of remote sites to poll, that can be a pretty good chunk of time during which no other comms can really take place.

 

I will mention this to our distributor and see if this is something that can be added to RemoteConnect.

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-07-01 05:11 PM

In response to fcantrell
0 Likes
1
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-01 05:11 PM

Such developments can take quite a while however, so I'd recommend that you also start to put together a test case for something similar to the work around that I've proposed.

 

That way if the feature doesn't make it into RemoteConnect you're not left entirely high and dry..

 

You're aware that the Data Concentrator feature is a licensed addition with the new RemoteConnect environment?

I can't remember where the break-point is in terms of slave count, my recollection was that a small number of slaves was allowed without a license, but over a certain number it did require a license for the RTU to perform the functionality.

I'm not sure if this was the case with the Telepace environment.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

fcantrell
Ensign fcantrell
Ensign

Posted: ‎2020-07-02 11:43 AM

In response to BevanWeiss
0 Likes
0
2929
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:43 AM

Thanks BevanWeiss. I will definitely do some bench testing to test a workaround like you suggested. Yes, I am aware that the Data Concentrator is a licensed feature but I don't have any specifics on that yet as far as cost, slave counts etc. I will check that out with our supplier,

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore