[Imported] Troubleshooting problems on a radio system

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • [Imported] Troubleshooting problems on a radio system
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
Trio Licensed Radios

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Remote Operations Forum
Start a Topic
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-10-25 12:20 PM

0 Likes
3
2622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-10-25 12:20 PM

[Imported] Troubleshooting problems on a radio system

>>Message imported from previous forum - Category:Trio Data Radios<<
User: joelw, originally posted: 2018-10-16 21:38:36 Id:32
This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.

------------------

**_jweder:
When looking for the source of poor or intermittent communication in a radio system, there are many potential failure sources. Here are a few suggestions for how to proceed when the problem isn't something you can solve quickly. Feel free to hit Reply and post some of your own suggestions!_**

_________________________________

Do you know how to use TView+ Diagnostics? Make sure you do (and that you have a copy installed) before you go to site! Run it to poll all the radios from the Master site. Look for high VSWR, low power supply voltage, incorrectly programmed Tx power etc.

Record the RSSI (received signal strength indication) for every remote site. Compare that against the radio's Rx sensitivity. (See the list at the bottom for sensitivity for all Trio models) All paths should have 20 dB of fade margin or more. Eg if K Series radios are programmed for 32 kbps radio data rate they have -108 dBm sensitivity. To have 20 dB fade margin each path would need -88 dBm RSSI or higher. (This may need to be higher if the local noise floor is stronger than the radio's receive sensitivity)

If fade margins at some sites are significantly below 20 dB, reduce the radio data rate (in ALL radios!) to 32 kbps (K Series) if not already there and if the user application allows it. (or 256 kbps instead of 512 kbps in J Series)
Check the antenna aiming for installation errors. Take a compass (with declination properly set!) and check aiming against the path study recommendation, if a study was done.

If antenna aiming is suspected as a problem, poll the radio (eg Individual Poll) while it's listening to its Master. Or if there's no radio traffic at the time poll the Master from the remote to cause traffic. Slowly move the Yagi antenna left/right to see if signal can be improved. (note that Individual Poll only updates every 2 seconds, so move the antenna a bit then wait for it to update)

If VSWR at any site is high (above 2 is a concern, but above 3 is a real problem) look for a damaged or incorrect type antenna, damaged or incorrect coax (must be 50 ohm type), damaged, loose or improperly installed connectors, or a bad surge arrestor. (polyphaser) This may require swapping out the antenna or coax (including jumper from radio to polyphaser) with a known good replacement.

Get permission to shut the system down for a few minutes (if possible) then run the spectrum analyzer at the Master. (If K or J Series) Look for any nearby strong signals that might be causing interference. Eg some cell towers are in the 850 MHz band and can cause problems if very near, and some paging systems are in the 950 range. A bandpass filter can be purchased and installed at the site near the interference source.

Run the spectrum analyzer at the most problematic remote sites. The master won't stop transmitting though, so you'll see some of its transmissions as it hops around. But still usually it's fairly apparent if there's a lot of interference or if the noise floor is higher than normal. If possible power down the Master while doing this to avoid seeing its transmissions.
Make sure the Master antenna is high and in the clear, and that the VSWR is low when running diagnostics. (VSWR for all sites should be under 2)

Was a path study done to calculate antenna heights or were they guessing? If no study was done, it might be necessary to do one or to modify antenna heights or types and/or convert some sites to Bridges.

Try bypassing the polyphaser at each site, most importantly at the Master. You may need a double-female adapter to tie the two cables together, or another polyphaser would of course work. These devices do become very lossy if they have absorbed lightning strikes or nearby surges.

Check all external coax cable connections to ensure they are thoroughly waterproofed. Water in a coaxial cable will cause power loss and seemingly low (not high!) VSWR.

At the remote sites, look for obstacles nearby in the path towards the Master. Eg a lot of trees nearby or a metal building. The antenna may need to be moved up to reduce losses. An additional 5-10 feet is often enough though on some obstructed paths the RSSI might actually get worse. In such a case try moving the antenna even further up, or in some cases moving it below the original height might help.

Do you know the protocol being used? Check the serial port config at each site to ensure the correct packet layer is chosen, especially if it's Modbus!

Check all communication cables to ensure nothing's loose and that they are the correct type. Also look for high voltage cables nearby that could induce hum on comms cables.

Don't forget to check the power supplies, as always! K Series needs 12-24 volts approximately, and the output should stay steady even while transmitting & drawing about 500 mA at 12 volts.

If a path remains weak a path study may need to be done to calculate a required antenna height. To do this make sure you have accurate GPS coordinates for all sites involved, note accurate tree heights and other obstacles near any of the sites. Fill out the path study request form, found on the Control Microsystems website (completely!!) then send it to TRSSpathstudy[at]schneider-electric.com.

Alternately you may reconfigure a nearby Remote as a Bridge (store & forward repeater) and aim the problem site's antenna at that site. This would require either changing the antenna at the Bridge site to an omni (if its path is strong enough to handle the 5+ dB reduction in signal strength this will cause) or an omni may be added to the ANT2 port and the Bridge set to Dual Antenna mode. (If J or K Series) In some cases where two sites are very close (eg under 1 km and no big obstacles between them) the Bridge may pick up the Remote's signal off the back or side of its yagi.

Labels
  • Labels:
  • Radio
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-10-25 12:21 PM

0 Likes
2
2621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-10-25 12:21 PM

>>Responses imported from previous forum


Reply From User: joelw, posted: 2018-10-16 21:38:48
Receiver sensitivity for Trio radio models:

K Series
256 kbps -102 dBm
128 kbps -104 dBm
64 kbps -106 dBm
32 kbps -108 dBm

J Series
512 kbps -92 dBm
256 kbps -102 dBm

E Series
9600 bps -108 dBm
19k2 -96 dBm 12.5 kHz radio
19k2 -106 dBm 25 kHz radio (not approved for North America)

M Series
9600 bps -106 dBm

-------------------------
Joel A. Weder
SCADA & Telemetry Solutions Specialist
Schneider Electric

Reply

Link copied. Please paste this link to share this article on your social media post.

michael_RID
Crewman michael_RID
Crewman

Posted: ‎2022-12-01 09:55 AM

In response to sbeadle
0 Likes
1
1941
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-01 09:55 AM

Receiver sensitivity for Trio Q radio models?

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

MartinChartrand
Captain MartinChartrand Captain
Captain

Posted: ‎2022-12-01 10:38 AM

In response to michael_RID
0 Likes
0
1935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-01 10:38 AM

Hello Mike,

If you go to this BLOG post, you'll find a downloadable EXCEL file that gives you links to all of our datasheets on the global website. At the bottom of the list are the Trio Q datasheets: QB, QH, QP and QR. On these datasheets, you'll find the most recent specifications for Receiver Sensitivity on those radios.

 

https://community.se.com/t5/Remote-Operations-Blog/Remote-Operations-Datasheets-Global-Website-Downl...

 

 

Thank you.

Martin

 

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore