[Imported] Grounding Issues - Antennas, Towers, Cabinets...

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • [Imported] Grounding Issues - Antennas, Towers, Cabinets...
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
Trio Licensed Radios

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Remote Operations Forum
Start a Topic
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-10-25 03:20 PM

0 Likes
1
1146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-10-25 03:20 PM

[Imported] Grounding Issues - Antennas, Towers, Cabinets...

>>Message imported from previous forum - Category:Trio Data Radios<<
User: joelw, originally posted: 2018-10-17 22:17:01 Id:115
This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.

-------------------

**_jweder:
There's a general lack of understanding of how to provide lightning protection for radios, antennas and towers. Many installers either ignore the issue, do the minimum possible, or sometimes even cause significant problems with their installation. Below is a brief discussion of common issues._**

1) Typically the antenna itself does not need to be grounded by the installer. The antenna is mounted with a metal clamp on a metal pole, which must be grounded.

2) If the antenna is a yagi, (directional type) it's a good idea to mount the antenna several feet below the top of the mast (spacing at least equal to antenna's length) to allow the mast to take the main hit on a lightning strike.

3) If the antenna is an omnidirectional type it's often mounted at the very top, though some are mounted on arms 2-3 feet out on the side of a tower. Many of these types are "DC grounded" which means the radiating element goes thru a coil to ground, allowing static buildup to be bled off as it tries to develop. This is often sufficient, but in some very heavy lightning areas installers may run a lightning rod around the omni and a few feet above. It must be kept well away from the antenna (a couple of feet) so it's a bit awkward but hardware does exist.

4) If the tower is tall a cable grounding clamp should be installed every (approx) 75 feet which grounds the coax outer shield to the tower itself. This bares the outer shield (braid) so care must be taken to waterproof the cable/clamp afterwards.

5) A good quality surge arrestor (eg polyphaser) must be used at the building entrance. It may be mounted in a metal feed-through plate, may be a simple in-line type, but must be connected to a heavy gauge ground cable or strap.

6) The ground cable from the surge arrestor must be heavy green ground cable, kept as short and straight as possible with NO coils and no sharp bends. These add inductance, which acts as a resistance to the high frequency energy of a lightning strike.

7) Ground cables must not run through metal conduit. This adds impedance and can pick up noise.

😎 Be aware that surge arrestors will fail after a period of time, either from absorbing one big surge or multiple smaller surges. This may appear as either an open circuit or more commonly as a source of high VSWR. (reflected power) Keep a spare handy and try swapping out the unit at site if high VSWR is seen.

9) A surge arrestor is not truly a lightning arrestor. A direct hit to the antenna may send enough energy through the system that the arrestor is overwhelmed, causing serious damage to the radio and attached equipment. A surge arrestor is primarily aimed at bleeding off the buildup of static charge to prevent a lightning strike in the first place.

10) The ground cable must go to an industrial quality ground rod or plate, installed according to local regulations or better. This must be an 8 or 10 foot rod.

11) All grounds should go to a common point eg a metal plate at the building cable entry point. Daisy-chained ground connections must be avoided.

12) The mast (if short eg 10-20 ft) must be grounded at the bottom with a short straight cable to a ground rod. Preferably a separate one but at a site where a short mast and the cabinet are close together often one rod is used.

13) If a small antenna structure is used a single long ground rod may be used at its base, but for a normal tower a ground ring should be installed with 3 or more ground rods, a ring of heavy copper wire connecting them, and several cables running out from the tower.

The above comments are general in nature. Several very good websites exist with far more information about grounding procedures and hardware. A quick Google search should find plenty of good reading.

-------------------------
Joel A. Weder
SCADA & Telemetry Solutions Specialist
Schneider Electric

Labels
  • Labels:
  • Radio
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-10-25 03:20 PM

0 Likes
0
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-10-25 03:20 PM

>>Responses imported from previous forum


Reply From User: joelw, posted: 2018-10-17 22:18:37
One item our company has discovered helps to minimize lightning strikes by controlling the dissipation of Ioninc particles. A typical dissipator will have at least 36+ points of dissipation per rod. Where dissipation has been deployed the number of strikes decrease dramatically or are eliminated.

-------------------------
Bill Parker/KC5UZE/EM#22


Reply From User: joelw, posted: 2018-10-17 22:18:56
When entering a building that already has a system ac ground rod installed is it better to install a separate ground rod and use it for the antenna or tag on to the existing ground as close to the main connection as possible? I've seen both installs at various sites and always wondered if it wad good to introduce a second ground rod in a building with an ac system ground already


Reply From User: joelw, posted: 2018-10-17 22:19:18
I would typically provide a separate ground rod (or plate) for antenna system grounding, presuming it's more than a very short distance away from the existing ground rod. I've seen sites where the tower has a ground rod (or more), the cable entry point has another, and the incoming electrical utility a third.

You may want to tie them all together with a heavy gage buried cable if the site is prone to lightning issues.

-------------------------
Joel A. Weder
SCADA & Telemetry Solutions Specialist
Schneider Electric

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore