[Imported] Ethernet Diagnostics In Trio Radios

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • [Imported] Ethernet Diagnostics In Trio Radios
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
Trio Licensed Radios

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Remote Operations Forum
Start a Topic
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-10-25 12:30 PM

0 Likes
0
1183
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-10-25 12:30 PM

[Imported] Ethernet Diagnostics In Trio Radios

>>Message imported from previous forum - Category:Trio Data Radios<<
User: joelw, originally posted: 2018-10-16 21:53:51 Id:40
This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.

--------------------

jweder:
All Trio data radios may be polled locally for diagnostic information, or remotely if installed in a working system. In a serial network (Ex450, MR450 or K Series) the System port is used. With a J Series radio, serial port B may be easily configured to act as a System port. However it is more common today to perform diagnostics of Ethernet-based radios using a LAN connection.

Trio has two radios with Ethernet capability - the J Series 900 MHz/2.4 GHz unlicensed radio and the E Series (Ex45e) licensed 400 MHz band radio. Ethernet diagnostic configuration works the same for both products, though the interface is different.

It must first be decided which radio will be the Diagnostics gateway into the radio network, to which the Diagnostics PC will be directly connected. This is the only radio which should have the "eDiags" feature enabled. This radio will forward messages to other radios using Trio's unique Diagnostics protocol.

**Ex45e Radio Configuration**:
Open the TView+ Management Suite
Select the E Series Programmer
Connect to the gateway radio serially and click Read (local radio)
Click on Diagnostics Setup
Click the checkbox to enable eDiags
Enter the IP address of the PC which will run the Diagnostics software
The default local and controller IP port number of 1040 should be acceptable
Click Ok, save the configuration, then click Write to send it to the radio

**JR900/JR240 Radio Configuration**:
Open a web browser
Connect an Ethernet cable to the gateway radio
Enter the IP address of the gateway radio
Click on the Setup menu
Select the eDiags configuration page
Click the Enable button
Enter the IP address of the PC which will run the Diagnostics software
The default local and controller IP port number of 1040 should be acceptable
Click Activate Configuration
Once the configuration changes have been activated, save the configuration

**TView+ Diagnostics Software Configuration**:
Open the TView+ Management Suite
Select the Diagnostics software tool
In the Settings menu, select eDiags Port Settings
Enter the PC's own IP address in the Local IP setting
The default eDiags port number of 1040 should be acceptable
Click Apply Changes and then Exit
In the File menu, select New
Choose a location to save the radio database and enter a name, then click Save
In the database dialog which appears enter the name and serial number of the gateway radio
Select the appropriate radio model
Select eDiags (Ethernet) for the Communications Port
For the Remote IP address enter the IP address of the gateway radio
The default Remote Port Number of 1040 should be acceptable
Modify the Alarm Limits for your radio system if desired
Click Apply Changes To Database
To add more radios click Add New

Other radios may be added in the same manner, but always specifying the IP address of the radio which is the Diagnostics gateway into the radio system. All other radios must be added in the same manner. In all cases enter the IP address of the "gateway" radio to which the Diagnostics PC is directly connected, not the IP address of the new radio being added. The Access Point is often the Diagnostics gateway to the radio system.

If it is desired to connect the TView+ Diagnostics PC to a Remote radio this is allowable. In that case eDiags must be enabled only in that Remote radio and not the Access Point. Also then the Remote radio's IP address would be used in each database entry.

In an E Series system, if a radio other than the Access Point is used as the Diagnostics gateway, the Access Point radio's Repeat Diagnostic Messages parameter must be enabled.

CAUTION: If eDiags is enabled in more than one radio in a system this may cause extra unwanted traffic which will reduce the available bandwidth for user data.

Labels
  • Labels:
  • Radio
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore