Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

[Imported] Diagnostics thru back-to-back repeater not working

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • [Imported] Diagnostics thru back-to-back repeater not working
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
76
BevanWeiss
Spock BevanWeiss
20
sbeadle
Kirk sbeadle Kirk
17
MartinChartrand
Captain MartinChartrand Captain
15
View All
Related Products
product field
Schneider Electric
Trio Licensed Radios

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Remote Operations Forum
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-10-25 03:11 PM

0 Likes
0
679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-10-25 03:11 PM

[Imported] Diagnostics thru back-to-back repeater not working

>>Message imported from previous forum - Category:Trio Data Radios<<
User: joelw, originally posted: 2018-10-17 21:08:45 Id:106
This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.

-------------

VirgilNicklas
**_Hello, I have been working with Trio PADs [data radios] for a few months. Their use of streams comes in handy when one needs not to only pass data but also be able to monitor the RF network. I have an MR450 connected (via 232) to a server. This radio connects via RF to an ER450 which has another MR450 connected to its port 1 as well as an RTU on port 2._**

**_The server's radio has opposing freqs to the ER450 repeater unit. The MR450 on the repeater unit has a linking freq, which exchanges data with another site that has pretty much the same layout as the one I just described. Only difference is the outstation radio is connected to a PLC. After setting up the streaming of all the units in the network, the data managed to come through and the diagnostics for the area that is serviced by the repeater serving the server. However, the diagnostics through to the other area does not work. Is there something I am leaving out?_**

---------------------

jweder:
If you are having immediate problems, please contact our Tech Support team directly. This forum is not designed to provide quick responses. You can call them at 1-888-226-6876 or email them at SupportTRSS[at]schneider-electric.com.

Speaking generally though, what you are talking about here is called a back-to-back repeater, or a tail-end link. It consists of two pairs of radios, each pair operating on its own network, on a unique radio frequency (or pair of frequencies). This will work fine, as long as you manage possible interference issues at the repeater site. This requires:
- Significant frequency separation between the two systems eg 5 MHz AND
- Significant antenna separation eg one directly above the other by about 6 metres OR
- If a duplexer (3 port mechanical filter) is purchased and properly tuned, you can connect both radios to a single antenna.

If each radio network is operating properly, and then you connect user data ports of the two radios at the repeater site together with a 3 wire NULL (cross-over) modem cable, you will get user protocol data out at the Outstation. However, diagnostic data is different...

Diagnostic data is typically routed to each radio's internal processor when the configured Stream ID is seen on an incoming data packet. (typically 0) In the case of a back-to-back repeater we also want the diagnostic data to go between radios so it gets onto the second radio network. This data can NOT use the user data port, as the configured Stream ID is not correct.

Instead what you need to do is connect the System (programming & diagnostics) port of the two radios at the repeater site together. This requires a NULL cable, similar to the cable for the user protocol data. You must make a cable, as Schneider/Trio does not have one for sale. The user manual lists the System port pins.

**Radio 1____ Radio 2**
RxD ----- TxD
TxD

Labels
  • Labels:
  • Radio
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of