[Imported] Calculating important reflected power values

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Remote Operations Forum
  • [Imported] Calculating important reflected power values
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Captain Joel_Weder Captain
92
BevanWeiss
Spock BevanWeiss
24
sbeadle
Kirk sbeadle Kirk
17
View All

Recommended Forums

  • EcoStruxure Geo SCADA Expert Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
Trio Licensed Radios

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Remote Operations Forum
Start a Topic
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-10-25 12:01 PM

0 Likes
1
1721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-10-25 12:01 PM

[Imported] Calculating important reflected power values

>>Message imported from previous forum - Category:Trio Data Radios<<
User: joelw, originally posted: 2018-10-16 20:35:16 Id:16
This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum. The original posters' identities have not been included. Schneider Electric is not responsible for the content of these posts.

------------------------
When diagnosing problems in the feedline, surge arrestor (polyphaser) or antenna it's useful to know how to compare forward and reflected power. (if you don't have direct access to VSWR or a VSWR calculator) There are three VSWR points which are useful to remember:

**1.5:1 VSWR** VSWR in a well designed system will fall below this level
**2:1 VSWR** The point above which you need to start being concerned. Put in a bit of effort to fix this.
**3:1 VSWR** There is a definite problem and you need to fix it ASAP.

**NOTE:** TView+ Diagnostics just gives the number 1.5, 2, 3 or whatever. It does not include the ratio part ":1"

But how do we know where these points are if you don't have a VSWR calculator? There's a simple rule of thumb that can help. Start with the forward power in dBm, and subtract 6 dB. That will be the 3:1 VSWR point. Subtract 10 dB and you're at the 2:1 point. Or subtract 14 dB and you're at the 1.5:1 point. So for example in a K Series radio set to 30 dBm Tx power:

3:1 VSWR = 30 – 6 = 24 dBm (250 mW)
2:1 VSWR = 30 – 10 = 20 dBm (100 mW)
1.5:1 VSWR = 30 – 14 = 16 dBm (40 mW)

In a licensed radio system with the transmitter running at the usual 37 dBm here are the numbers to watch for:

3:1 VSWR = 37 – 6 = 31 dBm (1.25 W)
2:1 VSWR = 37 – 10 = 27 dBm (500 mW)
1.5:1 VSWR = 37 – 14 = 23 dBm (200 mW)

**VSWR = Voltage Standing Wave Ratio**, a comparison of forward wave voltage to reflected wave voltage. We don't really care how this is handled by calculators which use voltage. We're more interested in power because that's what our radios report.

The VSWR calculator available on the Times Microwave website can be really useful. There are lots of them online.

Here's another useful bit of information - the equation to **calculate dBm from power:**

dBm = 10 log (Power/1 mW) with Power measured in milliwatts. (the 1 mW point is 0 dBm)

If you want to calculate VSWR (eg in a program) from forward and reflected power, here's the equation:

VSWR = (1 + Sqrt (Prefl/Pfwd)) / (1 – Sqrt (Prefl/Pfwd)

And here it is more visually:
![]((see attachments below) aj/1yx2zrh5gsng.jpg "")

-------------------------
Joel A. Weder
SCADA & Telemetry Solutions Specialist
Schneider Electric

Attached file: (editor/aj/1yx2zrh5gsng.jpg), VSWR Calculation.jpg File size: 19448

Attachments
Labels
  • Labels:
  • Radio
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-10-25 12:02 PM

0 Likes
0
1719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-10-25 12:02 PM

>>Responses imported from previous forum


Reply From User: joelw, posted: 2018-10-17 15:39:57
Here's a simple program that helps calculate VSWR, or from VSWR and forward power you can work out reflected power.

Attached file: (editor/he/ucwyk61b1lg7.zip), vswrcalc.zip File size: 74306

Attachments
ucwyk61b1lg7.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore