Posted: 2021-03-22 04:31 AM
Hello,
No, the SCADAPack E-Series RTUs cannot be programmed with RemoteConnect. RemoteConnect is for the SCADAPack 57x and 47x RTUs only.
The E-Series RTUs are configured (Com ports, IO Assignment etc) by the "SCADAPack E Configurator", or logic-programmed with the "SCADAPack E Workbench" (IEC61131-3) platform. Both are available from Exchange Shop, here in a single download: https://shop.exchange.se.com/en-US/apps/62865/scadapack-e-workbench-and-utilities
Please note that although the download from Shop is free, you will need a purchased license to fully operate SCADAPack E Workbench. The "SCADAPack E Configurator" does not require a license.
Regards,
Martin Chartrand
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-22 03:17 PM
@MartinChartrand does 8.17.1a (and possibly latter) still require the explicit licence?
I noticed this on my latest installation when I went to jump through the licence hoops, and was instead greeted by:
I'm used to this just saying Engineering Trial Licence with an expiration of xx days.
Maybe this was a glitch, and if I 'upgrade' again to 8.18 then I lose this...
I assume there's no plans to have a migration firmware to allow an existing 3xx / 5xx SCADAPack to run x70 and utilise RemoteConnect? It's certainly a bit tricky, since with such a cold migration process our customers are typically jumping ship entirely... Why pay to migrate from a SCADAPack 3xxE series to a SCADAPack x70 when they could just as easily migrate to a Wago PFC200, Brodersen RTU32M, or Kingfisher CP35 platform?!?
Having a seam-free engineering migration pathway should have been a higher priority.
I would have thought the complaints when Schneider did the ISaGRAF v3 -> SCADAPack Workbench migration, and the huge numbers of customers that simply didn't follow this transition would have taught a lesson.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-23 11:08 AM
Hello,
Workbench no longer requires a license to run. It does, however, still require a license for the legal right to be used. The message that was displayed indicates that the software is installed in a working state with a license file that does not expire. This applies to any installation of 8.18.1 onwards.
There are no plans to allow a 3xxx/3xxE to run x70 firmware and use RemoteConnect; the hardware, unfortunately, cannot support such a path. However, we do intend to offer an automated conversion using the new EcoStruxure Control Engineering product. This system allows a user to provide their configuration and program to the ECE team who will provide an automated conversion to RemoteConnect. We have this capability available for the standard (e.g. Telepace-based SCADAPack RTUs) ready; it will be made available to customers in June 2021. You can expect the equivalent for Workbench this fall. Regarding the SCADAPack 53xE we are studying a potential conversion path to the SCADAPack 57x.
Thank you for your initial comments, they are much appreciated.
Martin
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-23 03:04 PM
@MartinChartrand wrote:...
You can expect the equivalent for Workbench this fall.
...
So in the next month or two? Given it's currently March, and fall/autumn is from March-May [here in AU] 😉
Or are you expecting it more in 2021Q3?
The 53x to 57x 'conversion' should have been trivial, since they are (were) exactly the same hardware. It should have simply been a case of allowing the common Bootloader to flash the x70 firmware regardless of existing firmware.
The E-series firmware is a little tricker given the ISaGRAF licence required (and WindRiver OS licence), but I expect there is a reserved non-volatile memory slot dedicated to serial number or similar which identifies whether the unit has been allocated an ISaGRAF licence (and hence can be flashed with E-series firmware).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-24 04:12 AM
I apologize for the seasonal confusion. 😁 Yes, we're looking at late Q3 2021 for the Workbench version of the ECE conversion product.
I will pass your subsequent comments on to the SCADAPack team.
Regards
Martin C.