Hi guys.
I used easergy studio to config for P139 Relay.
I want to create single diagram for HMI panel on relay screen. The easergy studio offers number of default type of bay, but No of them was suitable with my single diagram. How can i modify type of bay which difined in easergy.
Thank you.
Link copied. Please paste this link to share this article on your social media post.
To put the P139 in Loading Mode by Frontal Panel, you need:
1 - Out of service the relay;
2 - Press the Buttons "i" and "R". The relay will enter in the Loading Mode;
3 - By Easergy studio, you need put the transfer Mode connections as Default connections and Donwload the file.
I suggest, between steps 1 and 2, to send to the relay the number of the custom bay type to relay (settings 220.000). I had a problems when I send this parameters after the download of BTC.
Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Currently looking for a Support able to address your question.
Best
Link copied. Please paste this link to share this article on your social media post.
Hello @manhkhuong
You can create a customized bay by the Easergy Studio. For that you need follow some steps.
I have a guide that the CCC create to customers of Brazil and I will attach here. This guide is in portuguese, but is so graphic and easy...maybe you can use a translator for help you.
If you have any question or need help, please send me a message.
@Jean_Commeignes / @Omaelk , congrats for your action and knowledge networking.
Link copied. Please paste this link to share this article on your social media post.
Thank @Felipe.Cunha for your support.
Are there any problems with Demo Version?
When i started, i didnt license file, so I used BCT in Demo Version. And now , i cant find where to import license ?
Link copied. Please paste this link to share this article on your social media post.
Hi manhkhuong,
you need to get in touch with Karsten Kupke (karsten.kupke@se.com), responsible for the Operational Marketing of MiCOM P30, who is able to provide you with an internal license. For customers, this license is not free of charge, our price list shall provide a related price for it.
With BR
Link copied. Please paste this link to share this article on your social media post.
I guy. I created BCT file following the user guide. How can i send this file BCT to relay.
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
I switched relay into File transfer mode, but I cant test connect successfully to relay from easergy.
Help me?
Thank
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Help me please?
I cold restart relay micom p139.
I find the ip for iec was 0.0.0.0.
How can i change this ip from local panel HMI.
I tries to do this by ied configurator, but not successfull.
I use lan port for 61850
Link copied. Please paste this link to share this article on your social media post.
You cannot change IP from local HMI or with Studio (the "IEC: IP address" on HMI/Studio is just an information parameter ('read only')). Its value is set from the "IED Configurator" with Communications: IP Address, only.
Unfortunately, I have no experience how to do this via LAN port.
Link copied. Please paste this link to share this article on your social media post.
Oh. Do you know anyone that can help me this problem.
Thank
Link copied. Please paste this link to share this article on your social media post.
Once you have your device configured with valid IP address you could use Ethernet link for configuration transfer.
Which port are you connected to Eth A, Eth B or Eth C? The bottom one is Eth C and after cold restart it has to be 192.168.1.4. Have you tried this?
However please keep in mind that for BTC transfer you woud need front panel connection, file transfer mode which is used to transfer customised bay type, needs serial connection.
Link copied. Please paste this link to share this article on your social media post.
Hi @Chris_Bennauer ,
I followed steps in the video you prepared for BTC configuration of P139
Just got stuck at step 4"downloading using file transfere" and got the attached error massage, is it a common issue for BTC to happen as I tested the normal serial connection and it works just after switching to file transfer mode it doesn't work.
BR
Amr
Link copied. Please paste this link to share this article on your social media post.
Dear @Amr_Hesham,
Is the relay you are working on the new P139 (black hardware)?
Before you downloaded the BTC, did you put the relay out of service? and put it also, through the front panel, in transfer mode?
Regards,
Link copied. Please paste this link to share this article on your social media post.
Dear FELIPE @Felipe.Cunha
yes It is P139 Black Hardware and I tried to put the relay out of service and when switching the connection to file transfer (loading mode) - by setting it as a default connection - the attached massage appears but after testing the connection for sending BTC the error "msg id: -1029" appears.
Also how can I set the relay into transfer mode from front panel?
BR
Amr
Link copied. Please paste this link to share this article on your social media post.
To put the P139 in Loading Mode by Frontal Panel, you need:
1 - Out of service the relay;
2 - Press the Buttons "i" and "R". The relay will enter in the Loading Mode;
3 - By Easergy studio, you need put the transfer Mode connections as Default connections and Donwload the file.
I suggest, between steps 1 and 2, to send to the relay the number of the custom bay type to relay (settings 220.000). I had a problems when I send this parameters after the download of BTC.
Regards