Ask our Experts
Didn't find what you are looking for? Ask our experts!
Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.
Search in
Link copied. Please paste this link to share this article on your social media post.
Hello,
I need advice about the TCS function for an ACB trip coil (220VAC). The ACB panel doesn't have relay protection, but there is a requirement for the TCS function. The incoming panel has a module card with 12DI and 4DO available.
If I connect it as shown in the picture, will the TCS function work or not?
Please advice.
Thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Hello,
Such scheme is feasible with P5F30 - PowerLogic P5 digital inputs can be used with 90 to 230 VAC nominal voltage.
For techincal specification and also how to set up TCS scheme please refer to the available documentation -
PowerLogic P5
regards
Rudolf
Link copied. Please paste this link to share this article on your social media post.
Hello,
Such scheme is feasible with P5F30 - PowerLogic P5 digital inputs can be used with 90 to 230 VAC nominal voltage.
For techincal specification and also how to set up TCS scheme please refer to the available documentation -
PowerLogic P5
regards
Rudolf
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.