Trip circuit supervision at module 12DI 4 DO P5F30 for ACB trip coil 220VAC

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Trip circuit supervision at module 12DI 4 DO P5F30 for ACB trip coil 220VAC
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
16
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
12
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
supakit.mitnipat
Crewman supakit.mitnipat Crewman
Crewman

Posted: ‎2025-03-19 08:50 AM

0 Likes
1
139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-19 08:50 AM

Trip circuit supervision at module 12DI 4 DO P5F30 for ACB trip coil 220VAC

Hello,

I need advice about the TCS function for an ACB trip coil (220VAC). The ACB panel doesn't have relay protection, but there is a requirement for the TCS function. The incoming panel has a module card with 12DI and 4DO available.

If I connect it as shown in the picture, will the TCS function work or not?

Please advice.

 

Thanks in advance

Attachments
Labels
  • Labels:
  • PowerLogic P5
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Rudolf_Simon
Commander Rudolf_Simon Commander
Commander

Posted: ‎2025-05-08 01:36 AM

0 Likes
0
35
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-08 01:36 AM

Hello,

Such scheme is feasible with P5F30 - PowerLogic P5 digital inputs can be used with 90 to 230 VAC nominal voltage.
For techincal specification and also how to set up TCS scheme please refer to the available documentation - 
PowerLogic P5

regards 

Rudolf

See Answer In Context

Reply
Reply 1
Rudolf_Simon
Commander Rudolf_Simon Commander
Commander

Posted: ‎2025-05-08 01:36 AM

0 Likes
0
36
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-08 01:36 AM

Hello,

Such scheme is feasible with P5F30 - PowerLogic P5 digital inputs can be used with 90 to 230 VAC nominal voltage.
For techincal specification and also how to set up TCS scheme please refer to the available documentation - 
PowerLogic P5

regards 

Rudolf

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of