Sepam Error Code No.3
I've Sepam 87 for MV MOTOR but suddenly I Lost all Temperature Signals and I found ERROR CODE NO.3 on Sepam and RTD Fault and also there is red led is on at the temperature module MET148-2. I just follow the manual instruction like:
1- Change the temperature module MET148-2
2- Change RG45
I made all of this but the error still, but when I disconnect all RTD Sensor from MET148-2 the error is gone but of course RTD Fault still there and when I connect one RTD Also still no Problem
but when i add more than one the error come again
the attached photo from sepam when the error code is appeared
Please add of your explanation the setting file extract of the Sepam and the SAV report. I put in attachment the SFT SAV software to extract the SAV report.