Saitel DR & DP - How to explain "Check Before Operate" (and not "Select Before Operate")?

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Saitel DR & DP - How to explain "Check Before Operate" (and not "Select Before Operate")?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Commander Araceli_Monje Commander
43
Arun-kumar_PS
Commander Arun-kumar_PS Commander
21
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
Lucas_Orlandini
Lucas_Orlandini Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2025-04-15 01:02 PM . Last Modified: ‎2025-04-16 02:02 AM

0 Likes
2
2665
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-15 01:02 PM

Saitel DR & DP - How to explain "Check Before Operate" (and not "Select Before Operate")?

Hello Community!

 

I need some help about Saitel documentation. Our customer wants us to present some documentation about the Check Before Operate (not Select Before Operate).

 

The Check Before Operate would be all checks the Saitel Platform executes (not in protocol level) before executing a command, such as: hardware integrity, communication failure, equipment position, etc.

 

Best regards,

 

Lucas Orlandini

Labels
  • Labels:
  • Saitel range
Tags (5)
  • Tags:
  • CBO
  • Check Before Operate
  • english
  • Saitel DP
  • Saitel DR
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JuanRayo
Lt. Commander JuanRayo Lt. Commander
Lt. Commander

Posted: ‎2025-04-21 02:30 AM

0 Likes
0
2582
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-21 02:30 AM

"SM_DO16R-User Manual.pdf"----On page 21.

"HUe-User Manual.pdf" ---On page 60.
Basically Saitel DP and DR has the same way to manage commands that is why I add the DO module from DP and the head unit from DR.

 

Hope this could be helpful for you Lucas.

See Answer In Context

Attachments
Reply
Replies 2
JuanRayo
Lt. Commander JuanRayo Lt. Commander
Lt. Commander

Posted: ‎2025-04-21 02:16 AM

0 Likes
0
2584
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-21 02:16 AM

Hello Lucas!.

 

Thanks for contact us.

 

As you can guess there is not only one document that mention "check before operate" because that depends on multiple factors like the source of the command and the final destination. 

When the destination of a command is one of our SM_DO (SaitelDP) or AB_DO (Saitel DR) modules the hardware status is always taking into account before accepting or not any command from outside.

Local/Remote status is always considered internally to manage or deny any command.

Formulae/Isagraf is always available to customize the conditions to manage commands.

Many communication protocols consider quality bits before proceeding with commands as well.

 

Let me gather some documents to share with you.

Reply
JuanRayo
Lt. Commander JuanRayo Lt. Commander
Lt. Commander

Posted: ‎2025-04-21 02:30 AM

0 Likes
0
2583
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-21 02:30 AM

"SM_DO16R-User Manual.pdf"----On page 21.

"HUe-User Manual.pdf" ---On page 60.
Basically Saitel DP and DR has the same way to manage commands that is why I add the DO module from DP and the head unit from DR.

 

Hope this could be helpful for you Lucas.

Attachments
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore