Hi teams,
I want table full register list of P3U30 (register status ON/OFF circuit breaker,...)
Thanks very much
Link copied. Please paste this link to share this article on your social media post.
Hello
You can use EasergyPro to get the list of Modbus Register.
You can connect online to a product or create an offline configuration. In offline mode, select the Modbus protocol in the communication parameters and new lines will appear in the menu, it's the list of pages of modbus registers.
Best Regards
Link copied. Please paste this link to share this article on your social media post.
Hi,
Agree, its the best way as Christophe mention. Same goes for any other protocol as well.
Something available in m.vamp.fi, but the materials there are not updated frequently
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello
You can use EasergyPro to get the list of Modbus Register.
You can connect online to a product or create an offline configuration. In offline mode, select the Modbus protocol in the communication parameters and new lines will appear in the menu, it's the list of pages of modbus registers.
Best Regards
Link copied. Please paste this link to share this article on your social media post.
Hi,
Agree, its the best way as Christophe mention. Same goes for any other protocol as well.
Something available in m.vamp.fi, but the materials there are not updated frequently
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hi Lehto.
May you please share this file again?
Link isn't working anymore.
Ty
Link copied. Please paste this link to share this article on your social media post.
Hi Mateus,
Once I needed to controll the CB from the SCADA using the P3U30, I did it as below:
Created a logic (control/logic) as per attached photo.
This logic let you controll the DO of the device (to switch it on and off.
then I used the virtual input. The virtual input has the address:
Virtual Input 1 - 403427
Virtual Input 2 - 403428
So I createt 2 tags in the scada (16 bit unsigned) for open and close the CB.
When sending the command, you should make this tag ON for 2 sec and OFF again.