Full register list P3U30

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Full register list P3U30
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Commander Araceli_Monje Commander
43
Arun-kumar_PS
Commander Arun-kumar_PS Commander
21
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
SESA528
Commander SESA528 Commander
Commander

Posted: β€Ž2021-06-03 10:26 AM . Last Modified: β€Ž2023-05-30 10:01 PM

0 Likes
7
4392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2021-06-03 10:26 AM

Full register list P3U30

Hi teams,

 

I want table full register list of P3U30 (register status ON/OFF circuit breaker,...)

 

Thanks very much

Labels
  • Labels:
  • PowerLogic P3
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
ChristopheCasa
Lt. Commander ChristopheCasa Lt. Commander
Lt. Commander

Posted: β€Ž2021-06-04 12:26 AM

1 Like
4
4384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2021-06-04 12:26 AM

Hello

You can use EasergyPro to get the list of Modbus Register.

You can connect online to a product or create an offline configuration. In offline mode, select the Modbus protocol in the communication parameters and new lines will appear in the menu, it's the list of pages of modbus registers.

 

modbus.png

 

Best Regards

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Risto_lehto
Commander Risto_lehto Commander
Commander

Posted: β€Ž2021-06-04 02:32 AM

1 Like
2
4371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2021-06-04 02:32 AM

Hi,

Agree, its the best way as Christophe mention. Same goes for any other protocol as well.

 

Something available in m.vamp.fi, but the materials there are not updated frequently

Documentation Β» Welcome to Schneider Electric Vamp Ltd!

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 7
SESA528
Commander SESA528 Commander
Commander

Posted: β€Ž2021-06-03 11:44 PM

0 Likes
5
4389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2021-06-03 11:44 PM

HI Teams,

 

Pls help me. Thanks very much.

Tags (1)
  • Tags:
  • english
Reply
ChristopheCasa
Lt. Commander ChristopheCasa Lt. Commander
Lt. Commander

Posted: β€Ž2021-06-04 12:26 AM

1 Like
4
4385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2021-06-04 12:26 AM

Hello

You can use EasergyPro to get the list of Modbus Register.

You can connect online to a product or create an offline configuration. In offline mode, select the Modbus protocol in the communication parameters and new lines will appear in the menu, it's the list of pages of modbus registers.

 

modbus.png

 

Best Regards

Tags (1)
  • Tags:
  • english
Reply
Risto_lehto
Commander Risto_lehto Commander
Commander

Posted: β€Ž2021-06-04 02:32 AM

1 Like
2
4372
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2021-06-04 02:32 AM

Hi,

Agree, its the best way as Christophe mention. Same goes for any other protocol as well.

 

Something available in m.vamp.fi, but the materials there are not updated frequently

Documentation Β» Welcome to Schneider Electric Vamp Ltd!

Tags (1)
  • Tags:
  • english
Reply
SESA528
Commander SESA528 Commander
Commander

Posted: β€Ž2021-06-04 10:54 PM

0 Likes
0
4366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2021-06-04 10:54 PM

Hi @ChristopheCasa ,

 

Thanks for your information πŸ™‚ 

Tags (1)
  • Tags:
  • english
Reply
SESA528
Commander SESA528 Commander
Commander

Posted: β€Ž2021-06-04 10:55 PM

0 Likes
0
4365
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2021-06-04 10:55 PM

Hi @Risto_lehto ,

 

Thanks for your support. πŸ™‚ 

Tags (1)
  • Tags:
  • english
Reply
Mateus_A2
Mateus_A2
Cadet

Posted: β€Ž2025-01-08 05:19 AM

1 Like
0
2567
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2025-01-08 05:19 AM

Hi Lehto.

 

May you please share this file again?
Link isn't working anymore.

 

Ty

Reply
Mentor
Ensign Mentor
Ensign

Posted: β€Ž2025-04-22 04:54 AM

0 Likes
0
1854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2025-04-22 04:54 AM

Hi Mateus,
Once I needed to controll the CB from the SCADA using the P3U30, I did it as below:
Created a logic (control/logic) as per attached photo.
This logic let you controll the DO of the device (to switch it on and off.
then I used the virtual input. The virtual input has the address:
Virtual Input 1 - 403427
Virtual Input 2 - 403428
So I createt 2 tags in the scada (16 bit unsigned) for open and close the CB.
When sending the command, you should make this tag ON for 2 sec and OFF again.Address.pngLogic-CMD.png

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore