SEPAM B83 replacement Powerlogic P5 / P7

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • SEPAM B83 replacement Powerlogic P5 / P7
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Commander Araceli_Monje Commander
43
Arun-kumar_PS
Commander Arun-kumar_PS Commander
21
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
sesa211247_brid
Lieutenant sesa211247_brid Lieutenant
Lieutenant

Posted: ‎2024-05-03 12:56 PM

0 Likes
4
1227
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-03 12:56 PM

SEPAM B83 replacement Powerlogic P5 / P7

Dear Community, 

 

Is there any plan to replace the SEPAM B83 IED within the Powerlogic P5 / P7 range

 

until now there is no IED that replace the SEPAM B83 ! 

SEPAM B83 is very helpful when syncing 2 busbar using the ANSI27 protection on each parts of the busbar 

Labels
  • Labels:
  • Application cases
  • IEC61850
  • PowerLogic P5
  • PowerLogic P7
  • Sepam range
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Stefan_Scharf
Ensign Stefan_Scharf Ensign
Ensign

Posted: ‎2024-08-16 12:30 AM

0 Likes
2
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-16 12:30 AM

There is no 1:1 replacement for SEPAM B83. You can use PowerLogic P7 for this application e.g. Feeder application level 1 supporting 2x 3phase VT proxies or 2x 1ph VT proxies. Sync-check ANSI 25 is also available. However, sufficient number of VT inputs are needed, you can choose between two CT/VT module variants 5CT/4VT or 6CT/3VT - max two modules are possible.

See Answer In Context

Reply
Stefan_Scharf
Ensign Stefan_Scharf Ensign
Ensign

Posted: ‎2024-08-19 01:09 AM

1 Like
0
1014
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-19 01:09 AM

It is available. When using e.g. P7 Feeder 2x 3ph VT  and 2x 1ph VT proxies are supported which is meeting B83 requirement which is 2x 3V + 2x V0 acc to SEPAM catalog. You have to make sure that the needed CT/VTs are equipped. Up to two CT/VT moudles can be equipped.

See Answer In Context

Reply
Replies 4
Stefan_Scharf
Ensign Stefan_Scharf Ensign
Ensign

Posted: ‎2024-08-16 12:30 AM

0 Likes
2
1063
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-16 12:30 AM

There is no 1:1 replacement for SEPAM B83. You can use PowerLogic P7 for this application e.g. Feeder application level 1 supporting 2x 3phase VT proxies or 2x 1ph VT proxies. Sync-check ANSI 25 is also available. However, sufficient number of VT inputs are needed, you can choose between two CT/VT module variants 5CT/4VT or 6CT/3VT - max two modules are possible.

Reply
sesa211247_brid
Lieutenant sesa211247_brid Lieutenant
Lieutenant

Posted: ‎2024-08-17 03:25 PM

0 Likes
1
1041
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-17 03:25 PM

Thank you for your response,

but without 2 voltages inputs on the P7 we can not achieve the 27R function on each busbar.

as you know this function is mandatory to make sure that there in no remanent energy (voltage) coming from motors during the CB's switching.

this could be solved if the P7 can handle 6 VT inputs (3 on each busbar).

 

Hope our colleague from R&D will manage this in the near future. 

Reply
Stefan_Scharf
Ensign Stefan_Scharf Ensign
Ensign

Posted: ‎2024-08-19 01:09 AM

1 Like
0
1015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-19 01:09 AM

It is available. When using e.g. P7 Feeder 2x 3ph VT  and 2x 1ph VT proxies are supported which is meeting B83 requirement which is 2x 3V + 2x V0 acc to SEPAM catalog. You have to make sure that the needed CT/VTs are equipped. Up to two CT/VT moudles can be equipped.

Reply
sesa211247_brid
Lieutenant sesa211247_brid Lieutenant
Lieutenant

Posted: ‎2024-08-19 01:34 AM

0 Likes
0
1005
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-19 01:34 AM

Thank You 

I'll check-it

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore