Has anyone done the integration between the SAITEL DP and the siemens SICAM PAS software using the 61850 protocol? When i try to import the .cid file from saitel I get error, even though the file has been validated by Schneider EPAS-E and Siemens system configurator.
Link copied. Please paste this link to share this article on your social media post.
Hello Jean-Yves.
For the benefit of any other interested on this topic I would say that eventually Sicam Pas supports only edition 1 of the norm for the scd file.
During the validation process of our scd file with Siemens software and based on a log message reported by them we had to:
1. remove "gi" from TrgOps because:
Log message:
2024-08-06 13:50:28 Warning: XERCES: Error at line 10427, char 85 --> '<TrgOps dchg="true" qchg="true" dupd="true" period="true" gi="true" />'
Info: (XERCES: 'Message: Attribute 'gi' is not declared for element 'TrgOps'')2.
2. we aIso removed that data class "SAV" after checking that was not relevant for our server side because this error message:.
2024-08-07 14:15:12 Warning: Common data class 'SAV' not supported.
2. We finally had to add one more Report Control Block instance for every dataset because another error message received not enough clear for me but clarified later by them.
Once we adapted our server side data model to these requirements they somehow validated the scd and sent me the final scd file in edition 2 (totally unexpected) so we finally integrated the file in our project to keep going with the project.
Customer First
Link copied. Please paste this link to share this article on your social media post.
Hello. Sorry for delay but ... you know.....summer holidays .
Please share with us saitel Easergy Builder configuration and the cid file to be integrated within saitel.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Thank you very much for your support in this case. Through your help and insistence we were able to move forward with testing this integration.
Link copied. Please paste this link to share this article on your social media post.
Thanks for your reply.
We have had to adapt our saitel´s data model to the sicam pas need´s.
It was tricky but happy to know that you keep moving forward with your project.
BR
Link copied. Please paste this link to share this article on your social media post.
Hello @JuanRayo , could you please detail the solution here so that it can benefit others?
Thank you!
Link copied. Please paste this link to share this article on your social media post.
Hello Jean-Yves.
For the benefit of any other interested on this topic I would say that eventually Sicam Pas supports only edition 1 of the norm for the scd file.
During the validation process of our scd file with Siemens software and based on a log message reported by them we had to:
1. remove "gi" from TrgOps because:
Log message:
2024-08-06 13:50:28 Warning: XERCES: Error at line 10427, char 85 --> '<TrgOps dchg="true" qchg="true" dupd="true" period="true" gi="true" />'
Info: (XERCES: 'Message: Attribute 'gi' is not declared for element 'TrgOps'')2.
2. we aIso removed that data class "SAV" after checking that was not relevant for our server side because this error message:.
2024-08-07 14:15:12 Warning: Common data class 'SAV' not supported.
2. We finally had to add one more Report Control Block instance for every dataset because another error message received not enough clear for me but clarified later by them.
Once we adapted our server side data model to these requirements they somehow validated the scd and sent me the final scd file in edition 2 (totally unexpected) so we finally integrated the file in our project to keep going with the project.
Customer First
Link copied. Please paste this link to share this article on your social media post.
Great thanks, Juan Jo!
Link copied. Please paste this link to share this article on your social media post.
Disculpa que versión de firmware en Saitel estabas trabajando? yo trabaje con la 11.06.14 y Easergy Builder 1.6.4, he trabajado con estas versiones y no he tenido problemas.