Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.
Search in
Please select a country to continue with beta search.
Link copied. Please paste this link to share this article on your social media post.
Hello everyone,
I am trying to test the residual overcurrent protection on a MiCOM P132 with FW 671 but it´s not working. It seems that something is blocking the start. The phase overcurrent was already checked and, it works fine. Perhaps there is something missing in the configuration (a screenshot of the configuration is attached).
Beforehand, thank you for your time.
Best regards,
Manuel Trebilcock
Link copied. Please paste this link to share this article on your social media post.
Hi,
Think you didn't enabled function on Parameters---Function Parameters--General functions--Main-- Syst. IN enabled USER.
THX,
Alin
Link copied. Please paste this link to share this article on your social media post.
Hi,
Think you didn't enabled function on Parameters---Function Parameters--General functions--Main-- Syst. IN enabled USER.
THX,
Alin
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.