Hello everyone,
I am trying to test the residual overcurrent protection on a MiCOM P132 with FW 671 but it´s not working. It seems that something is blocking the start. The phase overcurrent was already checked and, it works fine. Perhaps there is something missing in the configuration (a screenshot of the configuration is attached).
Beforehand, thank you for your time.
Best regards,
Manuel Trebilcock
Link copied. Please paste this link to share this article on your social media post.
Hi,
Think you didn't enabled function on Parameters---Function Parameters--General functions--Main-- Syst. IN enabled USER.
THX,
Alin
Link copied. Please paste this link to share this article on your social media post.
Hi,
Think you didn't enabled function on Parameters---Function Parameters--General functions--Main-- Syst. IN enabled USER.
THX,
Alin