PowerLogic T300 - integrated webserver on separate HMI

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • PowerLogic T300 - integrated webserver on separate HMI
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Commander Araceli_Monje Commander
43
Arun-kumar_PS
Commander Arun-kumar_PS Commander
21
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
Schneider Electric
PowerLogic T300

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
Mikel_Beltrán
Ensign Mikel_Beltrán Ensign
Ensign

Posted: ‎2021-11-30 07:09 AM . Last Modified: ‎2025-05-26 12:36 AM

0 Likes
2
1553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-30 07:09 AM

PowerLogic T300 - integrated webserver on separate HMI

Dear community,

 

we wonder if it is possible to have the web pages that make up the T300 webserver integrated on another website. For example, in a web platform such as EcoStruxure Building Operation (EBO), which is the case we are interested on.

 

We know that there is always the option of opening a new browser tab and accessing the webserver from there, but we are looking for a more elegant solution.

 

When testing the connection to the T300 webserver from the EBO web page, it rejects the connection for security reasons, since it does not allow access to its web server inside another web page. It is likely a cybersecurity issue, and it is the T300 itself that rejects the connection.

 

Is it possible to allow the T300 webserver content to be seen inside another web page?

 

Thank you very much!

 

Mikel

  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Labels
  • Labels:
  • PowerLogic T300
Tags (6)
  • Tags:
  • ebo
  • english
  • Modbus HMI on T300
  • t300
  • T300 webserver
  • webserver
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mikel_Beltrán
Ensign Mikel_Beltrán Ensign
Ensign

Posted: ‎2021-12-02 03:31 AM . Last Modified: ‎2021-12-02 03:31 AM

0 Likes
0
1540
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-12-02 03:31 AM

Dear Tom,

 

thank you very much for your perspective on the matter and for your quick response.

 

Given how challenging it is going to be to resolve this in the way I stated in my original post, we have decided to be selective with the T300 governed system variables we want to display on screen, assign them a Modbus address, and create an alternative interface (more modest than the original T300 webserver, but sufficient for the purpose we have).

 

The ideal outcome would have been to have the whole webserver interface as such, but I understand that it is a complicated task and whose solution is beyond the scope we have.

 

Thank you very much for your help.

 

Best regards,

 

Mikel

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
TomBerry
Lieutenant JG TomBerry Lieutenant JG
Lieutenant JG

Posted: ‎2021-11-30 07:29 AM

0 Likes
1
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-30 07:29 AM

I'll have to ask the product security office (PSO) what they advise but for me it seems prudent to only allow web pages on remote devices to be opened in a new separate window.

 

How much of the T300 web page functionality do you need?

I assume you want access to more information than can be retrieved by SCADA protocols, like settings.

 

It is feasible to write your own client application to display information retrieved using the same web services (and the same user login).

 

There are other products that do this, such as EcoStruxure™ Power Automation System Maintenance – EPAS-M

 

Tags (1)
  • Tags:
  • english
Reply
Mikel_Beltrán
Ensign Mikel_Beltrán Ensign
Ensign

Posted: ‎2021-12-02 03:31 AM . Last Modified: ‎2021-12-02 03:31 AM

0 Likes
0
1541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-12-02 03:31 AM

Dear Tom,

 

thank you very much for your perspective on the matter and for your quick response.

 

Given how challenging it is going to be to resolve this in the way I stated in my original post, we have decided to be selective with the T300 governed system variables we want to display on screen, assign them a Modbus address, and create an alternative interface (more modest than the original T300 webserver, but sufficient for the purpose we have).

 

The ideal outcome would have been to have the whole webserver interface as such, but I understand that it is a complicated task and whose solution is beyond the scope we have.

 

Thank you very much for your help.

 

Best regards,

 

Mikel

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore