I couldn't read double points from the PM2230 or another brand/model energy analyzer. There was no problem in the p2230 because there were 32-bit versions of 64-bit data but there is no such option in other brands.
PowerLogic T300 WebApp does not give any error: the value is always displayed as 0 (zero).
I believe I have done the definitions correctly but it doesn't work: can you help?
hu-250 firmware is V2.9.3-4542
Active Energy Delivered (Into Load) | Y | Y | Y | Y | Y | 3204 | Wh | 4 | INT64 |
I wrote 3203 because there is 1 offset in the register table
Link copied. Please paste this link to share this article on your social media post.
Hello,
could you please check the Modbus traces to see what is answered by the PM2230 ?
Can you see the value if you poll the PM2230 with another device (Modbus simulator) ?
The T300 version 2.9.4, coming soon, is managing new 64 bits formats (ULL and LL) that may match with your need (Wh = counter). But the D format you have used should give a value anyway.
Mathieu.
regards,
Mathieu.
Link copied. Please paste this link to share this article on your social media post.
Hello , it may be related with problem we solved in 2.9.4 release (Modbus counter 64bits) could you please test the new version?