Hello,
How do we use the VDS adapter with the Maxeta VDS, please? I found some info in the SC150 installation manual but it is still not clear to us.
Kind regards,
MC
Link copied. Please paste this link to share this article on your social media post.
Update from 2025-05-27
The two main types of VDS (VDS HR, VDS LRM) can be connected to PowerLogic SC150-CT/LPVT ref. EMS59201 using different adapters: EMS59580 for VDS HR, EMS59570 for VDS LRM.
Note: EMS59201 can now be connected to the new standard called VDIS using EMS570 adapter.
------------------
Hello,
Easergy SC150-CAPA voltage input is compatible with VDS (voltage detection systems) of type LRP, LRM and LR following the IEC 61243-5 standard (maximum admissible voltage: 30 Vac LL).
From Maxeta website, it seems that their VDS falls in that category so it should work.
To connect the VDS to Easergy SC150 voltage input, process as follows:
When the MV voltage is powered, Easergy SC150-CAPA will calibrate using the output of the VDS.
If you have done all that and that you have an issue, please clarify what exactly.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Update from 2025-05-27
The two main types of VDS (VDS HR, VDS LRM) can be connected to PowerLogic SC150-CT/LPVT ref. EMS59201 using different adapters: EMS59580 for VDS HR, EMS59570 for VDS LRM.
Note: EMS59201 can now be connected to the new standard called VDIS using EMS570 adapter.
------------------
Hello,
Easergy SC150-CAPA voltage input is compatible with VDS (voltage detection systems) of type LRP, LRM and LR following the IEC 61243-5 standard (maximum admissible voltage: 30 Vac LL).
From Maxeta website, it seems that their VDS falls in that category so it should work.
To connect the VDS to Easergy SC150 voltage input, process as follows:
When the MV voltage is powered, Easergy SC150-CAPA will calibrate using the output of the VDS.
If you have done all that and that you have an issue, please clarify what exactly.