Hi Team,
We have submitted a ticket to prepare the ETAP Library for the Power Logic P7 Relay.
The ETAP Technical team has raised some technical queries regarding this request, which are attached to this email.
Please provide your response as soon as possible.
Thanks,
Karthick C
Link copied. Please paste this link to share this article on your social media post.
Hi Karthick,
1. Regarding IDMT curves, considering Is the set threshold:
-The minimum trip level is 1.025 Is
Gregory_Meunier_0-1749677869427.png
- The level at which the tripping time becomes independent is 40 Is.
This is valid as long as measured currents are within the dynamic range of the CT inputs.
Gregory_Meunier_1-1749678122664.png
Gregory_Meunier_2-1749678247072.png
2. Regarding thermal overload and negative sequence overcurrent threshold, the Full load amps (FLA) parameter can be defined between 0.1 and 3.25 pu.
Link copied. Please paste this link to share this article on your social media post.
Hi Karthick,
1. Regarding IDMT curves, considering Is the set threshold:
-The minimum trip level is 1.025 Is
Gregory_Meunier_0-1749677869427.png
- The level at which the tripping time becomes independent is 40 Is.
This is valid as long as measured currents are within the dynamic range of the CT inputs.
Gregory_Meunier_1-1749678122664.png
Gregory_Meunier_2-1749678247072.png
2. Regarding thermal overload and negative sequence overcurrent threshold, the Full load amps (FLA) parameter can be defined between 0.1 and 3.25 pu.
Link copied. Please paste this link to share this article on your social media post.
Thanks Gregory.
I will share these answers with ETAP Technical team through Help Centre to prepare the Power Logic P7 Relay.