Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PowerLogic P7 Relay - ETAP Library Preparation

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • PowerLogic P7 Relay - ETAP Library Preparation
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Araceli_Monje Mentor
74
JuanRayo
JuanRayo Mentor
38
Arun-kumar_PS
Arun-kumar_PS Mentor
33
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
Karthick-507211
Karthick-507211 Leader
Leader

Posted: ‎2025-06-11 08:09 AM

1 Like
2
1264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-11 08:09 AM

PowerLogic P7 Relay - ETAP Library Preparation

Hi Team,

We have submitted a ticket to prepare the ETAP Library for the Power Logic P7 Relay.

 

The ETAP Technical team has raised some technical queries regarding this request, which are attached to this email.

 

Please provide your response as soon as possible.

 

Thanks,

Karthick C

@Sabhanayagan_Matheswaran 

 

 

Attachments
PowerLogic P7 Relay Queries.docx
Labels
  • Labels:
  • PowerLogic P7
Tags (2)
  • Tags:
  • english
  • sabha
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Gregory_M
Gregory_M Mentor
Mentor

Posted: ‎2025-06-11 03:08 PM

1 Like
1
1254
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-11 03:08 PM

Hi Karthick,

1. Regarding IDMT curves, considering Is the set threshold:
-The minimum trip level is 1.025 Is

Gregory_Meunier_0-1749677869427.pngGregory_Meunier_0-1749677869427.png

- The level at which the tripping time becomes independent is 40 Is.
This is valid as long as measured currents are within the dynamic range of the CT inputs.

Gregory_Meunier_1-1749678122664.pngGregory_Meunier_1-1749678122664.png

Gregory_Meunier_2-1749678247072.pngGregory_Meunier_2-1749678247072.png

 

2. Regarding thermal overload and negative sequence overcurrent threshold, the Full load amps (FLA) parameter can be defined between 0.1 and 3.25 pu.

 

See Answer In Context

Reply
Replies 2
Gregory_M
Gregory_M Mentor
Mentor

Posted: ‎2025-06-11 03:08 PM

1 Like
1
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-11 03:08 PM

Hi Karthick,

1. Regarding IDMT curves, considering Is the set threshold:
-The minimum trip level is 1.025 Is

Gregory_Meunier_0-1749677869427.pngGregory_Meunier_0-1749677869427.png

- The level at which the tripping time becomes independent is 40 Is.
This is valid as long as measured currents are within the dynamic range of the CT inputs.

Gregory_Meunier_1-1749678122664.pngGregory_Meunier_1-1749678122664.png

Gregory_Meunier_2-1749678247072.pngGregory_Meunier_2-1749678247072.png

 

2. Regarding thermal overload and negative sequence overcurrent threshold, the Full load amps (FLA) parameter can be defined between 0.1 and 3.25 pu.

 

Reply
Karthick-507211
Karthick-507211 Leader
Leader

Posted: ‎2025-06-11 07:55 PM

0 Likes
0
1250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-11 07:55 PM

Thanks Gregory.

I will share these answers with ETAP Technical team through Help Centre to prepare the Power Logic P7 Relay.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore