P3 have opiton to disable alarm to appear in Screen.
How this can be disable in P5. only option i can see is to disable it from event log but then it would not appear in event log.
Regards
Palak shah
Link copied. Please paste this link to share this article on your social media post.
Could you please add some more information?
What system is it, what version?
Link copied. Please paste this link to share this article on your social media post.
P5F30 latest firmware.
I would like to disable Alarm appearance in Screen. rather use LED assigned to protection and event log for detail.
Link copied. Please paste this link to share this article on your social media post.
Hello Palak,
unfortunately, such feature is not yet available in P5 (there are plans to enhance it, but not yet fully settled = too early to promise/announce it).
Idea behind this feature was to make user aware about protection operation (= starting/tripping events), which usually should not happen often in normal operation, but might be disturbing during testing or commissioning.
So today only option in P5 is really to disable the protection start/trip signals from event enabling (disconnect in matrix), with the well noticed drawback that then these events are no longer logged.
Notably, some events remain logged in the event list (like global trip, phase alarm and trip signals,...) but don't cause the alarm window on HMI.
It might be a trade-off possible, e.g. to keep just the trip ON events as major events?
best regards