P441 Relay Support

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • P441 Relay Support
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
22
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
13
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
manhkhuong
Ensign manhkhuong
Ensign

Posted: ‎2025-04-25 01:37 AM

0 Likes
3
142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-25 01:37 AM

P441 Relay Support

Dear Guys.

My plant has used P441 Relay for 5 years.

Recently, after Protection function happen occer, Leds on Relay lighted up.

I want to reset these indication, however i can't login to relay by password: AAAA.

The procedures like below

- I typed AAAA and push Enter Button.
- LCD inform that Pasword Entered Access level 1. And after then turn back to tpye password page.

ANyone can help me.

manhkhuong_0-1745570234716.png

 


Many thanks

Labels
  • Labels:
  • MiCOM range
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Arun-kumar_PS
Lt. Commander Arun-kumar_PS Lt. Commander
Lt. Commander

Posted: ‎2025-04-25 05:53 AM

0 Likes
1
120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-25 05:53 AM

Hello @manhkhuong 

It appears that the level 2 and level 3 passwords have been changed from the default "AAAA."

 

You will need at least level 2 access to reset the indication.

 

If you cannot recall or find the level 2 password, please contact SE technical support using the link below to create a support ticket. A support agent will assist you in obtaining the recovery password. You need supply details like relay model number, serial number, security code etc. 

 

 

https://www.se.com/ww/en/work/support/country-selector/get-support.jsp Select country and then select "Contact Center".  

 

See Answer In Context

Reply
Replies 3
Arun-kumar_PS
Lt. Commander Arun-kumar_PS Lt. Commander
Lt. Commander

Posted: ‎2025-04-25 05:53 AM

0 Likes
1
121
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-25 05:53 AM

Hello @manhkhuong 

It appears that the level 2 and level 3 passwords have been changed from the default "AAAA."

 

You will need at least level 2 access to reset the indication.

 

If you cannot recall or find the level 2 password, please contact SE technical support using the link below to create a support ticket. A support agent will assist you in obtaining the recovery password. You need supply details like relay model number, serial number, security code etc. 

 

 

https://www.se.com/ww/en/work/support/country-selector/get-support.jsp Select country and then select "Contact Center".  

 

Reply
manhkhuong
Ensign manhkhuong
Ensign

Posted: ‎2025-04-26 12:55 AM

0 Likes
0
87
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-26 12:55 AM

Dear Sir

Thank for your support

Can I use easergy studio connect to relay and reset indication in my case

Many thank.

Reply
Arun-kumar_PS
Lt. Commander Arun-kumar_PS Lt. Commander
Lt. Commander

Posted: ‎2025-04-28 09:56 PM

0 Likes
0
67
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-28 09:56 PM

Hello @manhkhuong 

Yes, Studio has functionality to reset the indication. You can try it. 

 

Arunkumar_PS_0-1745902398161.png

 

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of