Dear Experts,
We will integration RTU and P3U30 using IEC-61850. Finally All data metering and status appear normally in RTU. The Problem is when we try to command DO (object1) didn't work with notification 'Access-Violation' using IED Scout. I have make sure that relay ready in remote mode.
Would you give us some advice with this issue?
Thank You and Regards
Rizal
Link copied. Please paste this link to share this article on your social media post.
Hi @Juha ,
Thank you very much your advices, I have make sure all as your suggest but still not working. Finally i got the solution, I tried to downgrade the version of esetup easergy pro to version 3.8.0 and it's working normally.
Regards
Rizal
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hi Ms,
Please try to change "Originator Category" to "station-control". I usually use that one to give Scout a command.
Hope this is useful.
I'm glad to receive your feedback about this solution, or if you fixed it differently.
Link copied. Please paste this link to share this article on your social media post.
Hi @rizalul_arifin , thanks for you question.
There can be several different reason for this access violation message, like the following:
- control is performed to the same position as present one (open to open or close to close)
- operation is blocked in the relay (by the use of object blocking matrix)
- even if relay is in remote state local/remote event is blocked and then status in the server is local
- control command type is not in line with current control model (one step vs 2 step command)
BR
-juha-
Link copied. Please paste this link to share this article on your social media post.
Hi @Juha ,
Thank you very much your advices, I have make sure all as your suggest but still not working. Finally i got the solution, I tried to downgrade the version of esetup easergy pro to version 3.8.0 and it's working normally.
Regards
Rizal