Dear All
I’m working on a project the power feeder protection use P3 U30. And the vendor provide a data list on feedback and control using modbus tcp.
I’m managed to get all feedback and also send the control command using object1 in device. The modbus frame write using fc 6 and is observed success by wire shark. Also the select command is reset after execute command is sent. So I think the command is received by the device. However the circuit breaker is not act at all. Is there any settings to block communication command? Manual operate is Ok. And when testing communication command remote signal is showed at the display.
Link copied. Please paste this link to share this article on your social media post.
Hello:
What the status of the remote local ? it should be at remote to issue control command by communication.
Link copied. Please paste this link to share this article on your social media post.
Please help me Chunmei_Yang
Link copied. Please paste this link to share this article on your social media post.
Could you pls send the configuration file for investigation?
If you have wireshark communication record, pls send me together.
Link copied. Please paste this link to share this article on your social media post.
Hello chunmei_yang
I can't remote control the easergy p3u30 I did these steps but do you know what's wrong
Link copied. Please paste this link to share this article on your social media post.
Hello John:
Sorry I can not view the picture attached, my view as this:
Here is a demonstration of remote control procedure for your reference.
1,Current object1 state is '0' at open state, perform close select obj1, write 1 at register 2509:
2,After close selection response ok, then Perform execute operation obj1, write 1 at register 2510:
Then obj1 close command send successfully. the open process is same.
To be noted the necessary conditions for a successful control :
1, correct register address
2, Object state should at close when perform open control, at open when perform close control.
3, at remote condition.
If it still not work, Could you pls change another client to test the remote control function?
I hope these can help.
BR.
Chunmei
Link copied. Please paste this link to share this article on your social media post.
Can you provide your email address?
Link copied. Please paste this link to share this article on your social media post.
Hi John,
Please contact your local technical support so we can provide a dedicated answer to your issue.
https://www.se.com/ww/en/work/support/country-selector/contact-us.jsp
Link copied. Please paste this link to share this article on your social media post.
Sorry for the trouble. I can directly access the modbus register and manage it. The problem I am facing is how to set the power operation type