MiCOM P740 - PU and CU communication Capability

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • MiCOM P740 - PU and CU communication Capability
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
23
HenriGRASSET
Captain HenriGRASSET Captain
15
Rudolf_Simon
Commander Rudolf_Simon Commander
13
View All
Related Products
product field
PowerLogic
Easergy MiCOM P740

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
Sabhanayagan_Matheswaran
Crewman Sabhanayagan_Matheswaran Crewman
Crewman

Posted: ‎2025-05-12 11:02 AM

0 Likes
2
339
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-12 11:02 AM

MiCOM P740 - PU and CU communication Capability

Hi Team,

 

We are working in a tendering opportunity, were the client requirement is to have redundant Central Unit system for Busbar protection. As a standard practice, will use PU - CU communication via single fiber optic cable from Channel-1 of P742/P743 to P741 communication slot. If I follow the standard procedure, to achieve the redundancy I need to duplicate the system, which add more cost to project and there is spare constraint as well to mount the 2 x Peripheral units in switchgears.

 

Instead of proposing the duplicated system, each P742 / P743 has 2 communication channels at the relay slots, can we use 1 channel for 1 CU (Main-1) and 2nd Channel for 2 CU (Main-2). Theoretically since the PU address is same both the CU can able to read the same data and work as a Main-1 & Main-2. Is this functionally correct, does P742 / P743 is functionally can communicate to 2 CUs simultaneously both Read & Write.

Thanks,
Sabhanayagan

  • Thumbnail of Easergy MiCOM P740
    PowerLogic
    Easergy MiCOM P740
View products (1)
Labels
  • Labels:
  • Application cases
  • MiCOM range
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
HenriGRASSET
Captain HenriGRASSET Captain
Captain

Posted: ‎2025-05-15 07:13 AM . Last Modified: ‎2025-05-15 07:14 AM

0 Likes
0
280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-15 07:13 AM

Hello,

 

Even if on the communication boards there are two communication channels, it is not possible to use both at the same time and thus not possible to have redundancy.

“N-1” redundancy is to be immune to one component being faulty. Having only one Central Unit to redundant Peripheral units or Peripheral units connected to redundant Central units does not provide it.

This redundancy is often done using a P740 and a P746 (one box or three box mode) that requires much less IEDs and space and provides different types of algorithms.

 

Regards

EDISON Expert

See Answer In Context

Reply
Replies 2
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
Lt. Commander

Posted: ‎2025-05-15 02:45 AM

0 Likes
0
294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-15 02:45 AM

@HenriGRASSET , hi, could you please support with this question about P740?, thx.

Reply
HenriGRASSET
Captain HenriGRASSET Captain
Captain

Posted: ‎2025-05-15 07:13 AM . Last Modified: ‎2025-05-15 07:14 AM

0 Likes
0
281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-15 07:13 AM

Hello,

 

Even if on the communication boards there are two communication channels, it is not possible to use both at the same time and thus not possible to have redundancy.

“N-1” redundancy is to be immune to one component being faulty. Having only one Central Unit to redundant Peripheral units or Peripheral units connected to redundant Central units does not provide it.

This redundancy is often done using a P740 and a P746 (one box or three box mode) that requires much less IEDs and space and provides different types of algorithms.

 

Regards

EDISON Expert
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of