Hi everyone,
I’m working with a MiCOM relay and I have a question about the setting “Vec.gr.ends a-b PSx”.
The case is a Dyn1 transformer where the HV side is supplied in negative phase sequence. I’m also using the “Phase sequence” setting configured as A-C-B, with standard connections everywhere else.
I’ve gone through the manual several times, but it’s not clear to me whether in this case I should set “Vec.gr.ends a-b PSx” to 1, assuming the negative sequence supply is already accounted for by the A-C-B phase sequence setting, or if it should actually be set to 11.
Any clarification or experience on this would be greatly appreciated.
Thanks in advance!
Link copied. Please paste this link to share this article on your social media post.
Hello @Carlos5
The Vec.gr.ends a-b PSx should be configured as 1, in line to the transformer vector connection. The reverse phase sequence is not going to change this, the A phase will be in the same position irrespective of positive or negative phase sequence. The LV side connection should follow the same reverse phase sequence.