Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

MiCOM C264 - Specification of Secondary Systems and Devices, Control System RTU

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • MiCOM C264 - Specification of Secondary Systems and Devices, Control System RTU
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Araceli_Monje Mentor
74
JuanRayo
JuanRayo Mentor
41
Arun-kumar_PS
Arun-kumar_PS Mentor
33
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
Milica_Repac
Milica_Repac
Explorer

Posted: ‎2021-04-06 06:26 AM . Last Modified: ‎2023-05-30 10:04 PM

0 Likes
2
2427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-04-06 06:26 AM

MiCOM C264 - Specification of Secondary Systems and Devices, Control System RTU

Hello everyone,

 

I need help with tendering documentation listed below.

 

Functionality:

 

- Outputs: 

  Control: 

              - it shall be possible to adjust in parameter the length of pulse control separately for each relay contact (in the range of 500 - 20000ms, in at least 4 steps),

              - it shall be possible to adjust in parameter the length of permanent control separately for ech relay contact (in the range of 1-20 minutes, in steps of one minute),

              - it shall be possible to withdraw the permanent control on change of indication or by dispatcher action.

 

Parameterising:

              - The RTU shall provide for integrating the power measurements in time to counter format, with a periodicity adjustable in parameter (1, 5, 15 minutes).

 

Can someone tell me if MiCOM C264 meets above listed requirements?

 

 

Thanks in advance.

 

 

Labels
  • Labels:
  • Application cases
Tags (3)
  • Tags:
  • english
  • MiCOM C264
  • tendering
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
SESA161069_EF33
SESA161069_EF33 Troubleshooter
Troubleshooter

Posted: ‎2021-04-06 08:06 AM

1 Like
0
2423
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-04-06 08:06 AM

Hi Milica,

 

 

for all the required controls, the solution go with the configuration of an Isagraf automation in the C264.

From the received control coming from the HMI operator, the automation adapts the behaviour of the C264 outputs.

 

For example, on the substation HMI, several options of pulse or latched durations are given to the operator who select one of them. The selected duration is sent to the C264 as a setpoint to consider in the automation. Then the automation pilots the output (pulse or latched) to obtain the selected duration.

The amount of engineering work to consider depends direclty on the number of outputs to take into account.

The most reasonable solution is to avoid one independent set of durations for each output and to offer one or few sets of durations, each one applicable to several outputs. When the ouput needs to be activated, is duration follows the selected one for the set of duration to which it is assigned.

 

The output duration can be shorten by providing the operator a button to interrupt the output control on the substation HMI. The controls goes to the automation which stops then the output control.

 

The same type of automation principle applies to power measurement.

The C264,must be equipped with a TMU board to compute power and energy.

The duration setpoint is selected by the operator, from the substation HMI and the continous power integration (= energy value) is reset according to this duration.

 

You have to consider the relevant engineeing worload in you quotation (specification, configuration, tests, FAT)

 

 

Best regards,

Eric FIERFOL
Energy Business Automation COE
Lattes France

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
SESA161069_EF33
SESA161069_EF33 Troubleshooter
Troubleshooter

Posted: ‎2021-04-06 08:06 AM

1 Like
0
2423
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-04-06 08:06 AM

Hi Milica,

 

 

for all the required controls, the solution go with the configuration of an Isagraf automation in the C264.

From the received control coming from the HMI operator, the automation adapts the behaviour of the C264 outputs.

 

For example, on the substation HMI, several options of pulse or latched durations are given to the operator who select one of them. The selected duration is sent to the C264 as a setpoint to consider in the automation. Then the automation pilots the output (pulse or latched) to obtain the selected duration.

The amount of engineering work to consider depends direclty on the number of outputs to take into account.

The most reasonable solution is to avoid one independent set of durations for each output and to offer one or few sets of durations, each one applicable to several outputs. When the ouput needs to be activated, is duration follows the selected one for the set of duration to which it is assigned.

 

The output duration can be shorten by providing the operator a button to interrupt the output control on the substation HMI. The controls goes to the automation which stops then the output control.

 

The same type of automation principle applies to power measurement.

The C264,must be equipped with a TMU board to compute power and energy.

The duration setpoint is selected by the operator, from the substation HMI and the continous power integration (= energy value) is reset according to this duration.

 

You have to consider the relevant engineeing worload in you quotation (specification, configuration, tests, FAT)

 

 

Best regards,

Eric FIERFOL
Energy Business Automation COE
Lattes France
Tags (1)
  • Tags:
  • english
Reply
JYPOC
JYPOC Mentor
Mentor

Posted: ‎2021-04-06 10:59 AM

0 Likes
0
2420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-04-06 10:59 AM

Hi,

Please clarify the application: is it for a HV/MV substation, or a MV/MV switching substation or a secondary MV/LV substation?

If that is a primary substation then go for Saitel DP; if that is for a secondary substation, the most suitable offer is Easergy T300.

Regards.

BR - Jean-Yves
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore