IEC 61850 Station control on P139

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • IEC 61850 Station control on P139
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
22
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
13
View All
Related Products
product field
PowerLogic
Easergy MiCOM Px30 Series

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
ManuelTrebilcock
Lieutenant JG ManuelTrebilcock Lieutenant JG
Lieutenant JG

Posted: ‎2022-03-21 10:30 AM . Last Modified: ‎2023-05-30 10:02 PM

0 Likes
5
1550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-21 10:30 AM

IEC 61850 Station control on P139

Dear community, 

 

I am having problems integrating an Easergy MiCOM P139 via IEC 61850. Everything works fine but the control of objects. When you try to control objects via a simulator using remote-control, it works fine. But when you try to control objects using a GE RTU we have problems because first, you have to active the Loc.StaOper and then activate the command. 

 

We want to avoid the use of this sequence and do it directly with one command. Hoe can we set up the configuration to work using station control with just one command?

 

 

Best regards,

 

Manuel Trebilcock

  • Thumbnail of Easergy MiCOM Px30 Series
    PowerLogic
    Easergy MiCOM Px30 Series
View products (1)
Attachments
Labels
  • Labels:
  • Application cases
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AndreMelo
Commander AndreMelo Commander
Commander

Posted: ‎2022-03-21 11:01 AM . Last Modified: ‎2022-03-21 11:14 AM

1 Like
4
1548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-21 11:01 AM

Hi @ManuelTrebilcock 

 

 

You can use the MAIN: Inp.asg.interl.deact -  221.007 to disable the Local Remote interlock of the Controllable Object. However, the relay is working properly for the application.

 

A command via protocol is a remote command so the GE Rtu shall be configured to send the originator category (orCat) = remote-control or station-control. 

 

The orCat is a mandatory parameter and most of the RTU can configure that, I am pretty sure it is possible in the GE RTU as well or you can change it directly in the SCD.

 

OrCat value meanings:

orcat values.PNG

 

Here is one example in Saitel:

 

orCat.PNG

 

 

Best Regards

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 5
AndreMelo
Commander AndreMelo Commander
Commander

Posted: ‎2022-03-21 11:01 AM . Last Modified: ‎2022-03-21 11:14 AM

1 Like
4
1549
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-21 11:01 AM

Hi @ManuelTrebilcock 

 

 

You can use the MAIN: Inp.asg.interl.deact -  221.007 to disable the Local Remote interlock of the Controllable Object. However, the relay is working properly for the application.

 

A command via protocol is a remote command so the GE Rtu shall be configured to send the originator category (orCat) = remote-control or station-control. 

 

The orCat is a mandatory parameter and most of the RTU can configure that, I am pretty sure it is possible in the GE RTU as well or you can change it directly in the SCD.

 

OrCat value meanings:

orcat values.PNG

 

Here is one example in Saitel:

 

orCat.PNG

 

 

Best Regards

 

Tags (1)
  • Tags:
  • english
Reply
ManuelTrebilcock
Lieutenant JG ManuelTrebilcock Lieutenant JG
Lieutenant JG

Posted: ‎2022-03-21 01:43 PM

0 Likes
0
1537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-21 01:43 PM

Thank you @AndreMelo for saving me one more time. I really appreciate your help.

Tags (1)
  • Tags:
  • english
Reply
ManuelTrebilcock
Lieutenant JG ManuelTrebilcock Lieutenant JG
Lieutenant JG

Posted: ‎2022-03-21 01:49 PM

0 Likes
2
1535
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-21 01:49 PM

I have another doubt: according to the manual the signal "MAIN:Inp.asg.interl.deact" disables interlocking of control commands
for switchgear. So, does it mean that every interlock is going to be disabled, not only the local/remote?

Tags (1)
  • Tags:
  • english
Reply
AndreMelo
Commander AndreMelo Commander
Commander

Posted: ‎2022-03-22 01:37 AM

0 Likes
1
1530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-22 01:37 AM

Hi @ManuelTrebilcock ,

 

Yes, if it doesn't fit your application you can set a DROP OFF to disable just while the command is executing using logic. another way is for the GE person to send a by-pass interlock with the command. But if they are able to do that they might be able to configure the orCat.

 

I'm happy it helped you.

 

Best Regards

Tags (1)
  • Tags:
  • english
Reply
Michael_H
Lieutenant Michael_H Lieutenant
Lieutenant

Posted: ‎2022-03-22 05:56 AM

0 Likes
0
1526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-22 05:56 AM

All

 

If interlocking checking is enabled in the device configuration, then it is in the interest of the user to have controls been checked. It is not an acceptable solution to just disable interlocking checking for the acceptance of controls in general. If an erroneous control was executed and damage was created, SE will be held responsible for not having rejected that control.

 

Bypassing checks can only be provided exception based on the responsiblitiy of the user. If the configuration is modified as proposed below, a user statement is needed - in written - that he approves operation of switchgear without checks.

 

 

Easergy P30 firmware defaults to LocSta="false" meaning the acceptance of controls from remote (e.g. control center). For un-manned substations remote controls are the typical mode of operation. Personnel entering the site will need log in and force LocSta to "true" in order to control switchgear from an operator workplace at station level. The forcing of LocSta is part of the automation system. For controls locally from the P30 front panel, the IED can be set to local. All control are permanently executed under interlocking checking.

 

In order to facilitate the engineering of the automation system re. forcing of LocSta, an application oriented enhancement of the IED firmware has been proposed. This solution is not yet implemented in Easergy P30.

 

 

Best regards,

Michael

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of