Hi, recently we have purchased P741 and P743 for decentralised busbar protection and in order to configure the relays i need "Scheme Editor" and "Synaptic Tool".
As in latest revision of Easergy Studio only two tools are provided which are Dynamic synaptic and File Merger whereas the former two are essentially required for configuration of relays. Please provide the tools.
Link copied. Please paste this link to share this article on your social media post.
Hello,
As stated in https://community.se.com/t5/Protection-Control/Rules-for-MiCOM-P740-Busbar-protection/m-p/170215 only P740 competency center teams can engineer a P740.
The list of P740 competency centers are available at:
If you wish to create a P740 competency center, please send a request to me by mail.
Regards
Henri GRASSET
Link copied. Please paste this link to share this article on your social media post.
Hi,
Yes the CT ratio are defined in the peripheral units P742 or P743, then the primary values are published to central unit P741. Central unit uses only the primary values to calculate the differential current and to compare to threshold..
So the central unit does not require any change when you update the CT ratio in a P742 / P743
Regards
Link copied. Please paste this link to share this article on your social media post.
Hello,
As stated in https://community.se.com/t5/Protection-Control/Rules-for-MiCOM-P740-Busbar-protection/m-p/170215 only P740 competency center teams can engineer a P740.
The list of P740 competency centers are available at:
If you wish to create a P740 competency center, please send a request to me by mail.
Regards
Henri GRASSET
Link copied. Please paste this link to share this article on your social media post.
Hi, on a changer le rapport TC d'un depart ,comment faire pour le changer sur l'unité centrale p740 ou bien le changement sur l'unité péripherique p742 suffit. on dispose de p740 Merger et Dynamic synaptic , pouvez nous guider ou envoyer la procedure .
merci d'avance
Link copied. Please paste this link to share this article on your social media post.
Hi,
Yes the CT ratio are defined in the peripheral units P742 or P743, then the primary values are published to central unit P741. Central unit uses only the primary values to calculate the differential current and to compare to threshold..
So the central unit does not require any change when you update the CT ratio in a P742 / P743
Regards
Link copied. Please paste this link to share this article on your social media post.
Hi
we changed the CT ratio on the PU but idiff remains large
regards
Link copied. Please paste this link to share this article on your social media post.
Hello,
You are not allowed to work on a P740.
As already written above:
As stated in https://community.se.com/t5/Protection-Control/Rules-for-MiCOM-P740-Busbar-protection/m-p/170215 only P740 competency center teams can engineer a P740.
The list of P740 competency centers are available at:
Please contact one of them for support.
Regards
Henri GRASSET