Fault locator function - Easergy P3 U30

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Fault locator function - Easergy P3 U30
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Commander Araceli_Monje Commander
43
Arun-kumar_PS
Commander Arun-kumar_PS Commander
21
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
PowerLogic
PowerLogic P2

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-02-23 02:00 PM . Last Modified: ‎2023-05-30 10:01 PM

0 Likes
2
1059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-23 02:00 PM

Fault locator function - Easergy P3 U30

Hi,

 

In which types of MV grid regarding Neutral earthing is the fault locator function (Easergy P3) applicable?

 

Thanks in advance.

 

Easergy P3

  • Thumbnail of PowerLogic P2
    PowerLogic
    PowerLogic P2
View products (1)
Labels
  • Labels:
  • Application cases
  • PowerLogic P3
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Juha
Captain Juha Captain
Captain

Posted: ‎2021-02-28 11:27 PM

1 Like
1
1055
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-28 11:27 PM

Dear @Anonymous user,

 

the fault locator can be used for radially operated MV networks. For short circuit fault the network star point connection doesn't matter. It means, the fault locator can be used for all type of radially operated networks.

 

For earth fault distance location answer in not that simple anymore. In principle, the locator can be used for all type of network. Difficulties will arise from uncertainty of zero sequence impedance. For overhead lines the zero sequence impedance is not well know. For cable networks the zero sequence impedance is known more accurately.

 

BR

-juha-

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
Juha
Captain Juha Captain
Captain

Posted: ‎2021-02-28 11:27 PM

1 Like
1
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-28 11:27 PM

Dear @Anonymous user,

 

the fault locator can be used for radially operated MV networks. For short circuit fault the network star point connection doesn't matter. It means, the fault locator can be used for all type of radially operated networks.

 

For earth fault distance location answer in not that simple anymore. In principle, the locator can be used for all type of network. Difficulties will arise from uncertainty of zero sequence impedance. For overhead lines the zero sequence impedance is not well know. For cable networks the zero sequence impedance is known more accurately.

 

BR

-juha-

 

Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2021-03-01 11:55 PM

0 Likes
0
1043
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-01 11:55 PM

Dear @Juha, thank you for help.

 

Best regards,

 

Hasan Muftic

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore