Hello,
How do we use the VDS adapter with the Maxeta VDS, please? I found some info in the SC150 installation manual but it is still not clear to us.
Kind regards,
MC
Link copied. Please paste this link to share this article on your social media post.
Hello,
Easergy SC150-CAPA voltage input is compatible with VDS (voltage detection systems) of type LRP, LRM and LR following the IEC 61243-5 standard (maximum admissible voltage: 30 Vac LL).
From Maxeta website, it seems that their VDS falls in that category so it should work.
To connect the VDS to Easergy SC150 voltage input, process as follows:
When the MV voltage is powered, Easergy SC150-CAPA will calibrate using the output of the VDS.
If you have done all that and that you have an issue, please clarify what exactly.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Hello,
Easergy SC150-CAPA voltage input is compatible with VDS (voltage detection systems) of type LRP, LRM and LR following the IEC 61243-5 standard (maximum admissible voltage: 30 Vac LL).
From Maxeta website, it seems that their VDS falls in that category so it should work.
To connect the VDS to Easergy SC150 voltage input, process as follows:
When the MV voltage is powered, Easergy SC150-CAPA will calibrate using the output of the VDS.
If you have done all that and that you have an issue, please clarify what exactly.
Thank you
Posted: 2020-04-24 03:48 AM
Link copied. Please paste this link to share this article on your social media post.
Thanks!
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of