PowerLogic T300 - transfer between IEC 101 and IEC 104 communication links

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • PowerLogic T300 - transfer between IEC 101 and IEC 104 communication links
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
22
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
13
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
milica_dukic_
Ensign milica_dukic_
Ensign

Posted: ‎2020-09-29 06:16 AM . Last Modified: ‎2025-05-27 06:43 AM

1 Like
6
1329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-29 06:16 AM

PowerLogic T300 - transfer between IEC 101 and IEC 104 communication links

Hello everyone,

 

In my current T300 project, if the IEC 104 channel is broken then the IEC 101 one should start running.

  • Is there any setting that could be done in T300 in order to make this automatic (if IEC 104 link is down then IEC 101 should come up)?
  • Or this transfer between communication links should be SCADAs and/or modems' responsibility?

    Any suggestion would be helpful.

    Thank you in advance.


Labels
  • Labels:
  • Application cases
  • PowerLogic T300
Tags (6)
  • Tags:
  • easergy t300
  • english
  • IEC 101
  • IEC 104
  • PowerLogic T300
  • redundant communications
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
jean-luc_batard
Lieutenant JG jean-luc_batard Lieutenant JG
Lieutenant JG

Posted: ‎2020-11-02 11:47 PM . Last Modified: ‎2025-05-27 06:44 AM

0 Likes
1
1272
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-02 11:47 PM

Hi Milica

 

Would be very useful to know your real application case as requested by Jean-Yves

 

Is there any legacy habit there?

 

Generally speaking, it is SCADA/Client responsibility to switch from one channel to another: therefore there is no automatic switching for IEC104/ 101 at T300 level.

 

The link notion referred by Manuel is applicable to DNP3 protocol

 

 

Best Regards

Jean-Luc BATARD
Distribution Automation Senior Application Engineer

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 6
manuellison
Crewman manuellison Crewman
Crewman

Posted: ‎2020-10-02 12:06 AM

0 Likes
0
1313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-02 12:06 AM

Hi Milica,

 

In T300 catalogue, page 29 you can find:

 

Channel association - Links
Some control centers or IEDs support double channels. The functionality can be
different for each protocol. The links are associations of two channels and they are
used to identify a double channel. Two modes of channels switching are possible:
• AutoSwitch: used with slave protocols. When the active channel stops receiving,
it switches to the other channel, which becomes active
• SwitchByMaster: used with the master protocol, the HU250 controls the channel
switching. A periodic switching between channels can be defined in order to
verify channel state TIME_FORCE_SWITCH

Tags (1)
  • Tags:
  • english
Reply
JYPOC
Commander JYPOC Commander
Commander

Posted: ‎2020-10-02 12:32 AM

0 Likes
4
1310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-02 12:32 AM

Hello Milica,

 

Like always, the devil is in the details so please provide the following a drawing of your communication architecture (from remote SCADA/DMS/ADMS to Easergy T300), including what modems are used (on the IEC 101 and on the IEC 104 links).

 

Thank you

BR - Jean-Yves
  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Tags (5)
  • Tags:
  • easergy t300
  • english
  • IEC 101
  • IEC 104
  • redundant communication
Reply
milica_dukic_
Ensign milica_dukic_
Ensign

Posted: ‎2020-10-02 05:40 AM

0 Likes
3
1302
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-02 05:40 AM

@manuellison @JYPOC thank you  for your answers.

@JYPOC in attached pictures you can see the project of radio-link. I hope it would be helpful. 

Thank you in advance.

Attachments
Tags (1)
  • Tags:
  • english
Reply
JYPOC
Commander JYPOC Commander
Commander

Posted: ‎2020-10-02 08:45 AM

0 Likes
2
1295
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-02 08:45 AM

Thank you Milica,

 

What I was looking for in reality, is the logical communication architecture between the remote SCADA and the T300. 

 

In addition I don't see what is the IEC 101 link here (is it over TCP?).

 

Regards,

Jean-Yves

BR - Jean-Yves
Tags (1)
  • Tags:
  • english
Reply
jean-luc_batard
Lieutenant JG jean-luc_batard Lieutenant JG
Lieutenant JG

Posted: ‎2020-11-02 11:47 PM . Last Modified: ‎2025-05-27 06:44 AM

0 Likes
1
1273
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-02 11:47 PM

Hi Milica

 

Would be very useful to know your real application case as requested by Jean-Yves

 

Is there any legacy habit there?

 

Generally speaking, it is SCADA/Client responsibility to switch from one channel to another: therefore there is no automatic switching for IEC104/ 101 at T300 level.

 

The link notion referred by Manuel is applicable to DNP3 protocol

 

 

Best Regards

Jean-Luc BATARD
Distribution Automation Senior Application Engineer
Tags (1)
  • Tags:
  • english
Reply
milica_dukic_
Ensign milica_dukic_
Ensign

Posted: ‎2020-11-18 05:41 AM

0 Likes
0
1262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-18 05:41 AM

@JYPOC  Yes it is IEC101 over TCP/IP.

 

@jean-luc_batard  Thanks for this the information.

 

 

This is old SCADA system at it is still not clear what are the intentions of end customer with IEC101/104. We are still trying to clarify with them what is behind with "transfer link" part. All we know that they want to have two links main and backup: IEC101 serial, and IEC101 over TCP if we understood correctly.

 

Best regards and thank you very much for help.

 

Milica Dukic

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of