Easergy P5 Error code 0x847fd3e8

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Easergy P5 Error code 0x847fd3e8
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
16
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
12
View All
Related Products
product field
PowerLogic
PowerLogic P3

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
D_Austin
Crewman D_Austin
Crewman

Posted: ‎2022-09-09 07:23 AM . Last Modified: ‎2023-05-30 10:07 PM

1 Like
2
2238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-09 07:23 AM

Easergy P5 Error code 0x847fd3e8

Good day

 

I have a demo P5 I received from a Schneider Rep which gave me the Error Code in the title when I turned it on (see below)

I do not know the history of the device, this was the first time that I have turned it on.

 

P5F30 Error.jpg

 

I found the following maintenance message in the P5 user manual which is not particularly helpful.

 

Maintenance message.jpg

 

I did contact the rep who gave me the relay and they said they would submit my information to support.

In the mean time I'm hoping someone may know something about this error.

 

I attempted to connect to the relay with eSetup Easergy Pro via USB and Ethernet (after finding the IP Address using an IP Sacn), however I could not connect to the device.

 

I unfortunately do not know what Firmware version is installed.

 

My thanks in advance.

  • Thumbnail of PowerLogic P3
    PowerLogic
    PowerLogic P3
View products (1)
Labels
  • Labels:
  • PowerLogic P5
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Danilo_se
Ensign Danilo_se Ensign
Ensign

Posted: ‎2022-09-12 12:00 AM . Last Modified: ‎2022-09-12 12:22 AM

1 Like
0
2231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-12 12:00 AM

Hi,

I faced the same issue for several P5 relays. It's an error that comes out when P5 is power off for a long time, The time reference is lost and the date goes back to 1970. SE L3 support provided a tool to fix the problem. So, just wait for this tool from L3 (must be used only by SE , internal use).

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Tomasz_M
Lieutenant JG Tomasz_M Lieutenant JG
Lieutenant JG

Posted: ‎2022-09-13 12:37 AM

1 Like
0
2222
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-13 12:37 AM

Hi,

 

looks legacy issue with the old products remained not energaised for very long period of time.

 

Please contact CCC to get quick fix for this problem. 

 

rgd

Tomasz

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
Danilo_se
Ensign Danilo_se Ensign
Ensign

Posted: ‎2022-09-12 12:00 AM . Last Modified: ‎2022-09-12 12:22 AM

1 Like
0
2232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-12 12:00 AM

Hi,

I faced the same issue for several P5 relays. It's an error that comes out when P5 is power off for a long time, The time reference is lost and the date goes back to 1970. SE L3 support provided a tool to fix the problem. So, just wait for this tool from L3 (must be used only by SE , internal use).

Tags (1)
  • Tags:
  • english
Reply
Tomasz_M
Lieutenant JG Tomasz_M Lieutenant JG
Lieutenant JG

Posted: ‎2022-09-13 12:37 AM

1 Like
0
2223
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-13 12:37 AM

Hi,

 

looks legacy issue with the old products remained not energaised for very long period of time.

 

Please contact CCC to get quick fix for this problem. 

 

rgd

Tomasz

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of