Dear Expert,
Do you have any experience integration
Easergy P3 to Siemens Sicam Pas?
We found when loaded the CID file of Easergy P3 to Sicam Pas there is warning alarm "no free RCB in SCD file".
Could you please advise on this.
  • IEC61850
  • PowerLogic P3
Thiago_Carreiras
Ensign Thiago_Carreiras Ensign
Ensign
Posted: ‎2024-11-07 06:04 AM
776
Hi @Rendi.ardian ,
Currently If I'm not wrong Siemens Sicam Pas supports both edition 1 and 2 of IEC61850. Could you please confirm with version of Sicam Pas are you using? The last one that support both edtion should be V08.06.
Based on this, could you please confirm the IEC61850 edition are you working? Coud you please share the CID file and P3 settings file?
Try to remove from triggering Options the "General Interogation" and the "Integrity" options from BRCB and check if the tool will acept.
In the Sicam Pas, warning could not be a real problem, need to check if the IED was imported and if the RCB are there also.
BR
Thiago Carreiras
Rendi.ardian
Rendi.ardian
Cadet
Posted: ‎2024-11-07 11:52 PM
752
Hi @Thiago_Carreiras ,
I dont know yet about the Sicam Pas version, but it use Edition 1.
The Siemens person said the importerd CID is different with the relay file.
Attached is the file P3 setting and CID.
The work is at site, we are in the office now.
Thanks & BR,
Rendi
Seting and CID file P3.zip
Thiago_Carreiras
Ensign
Posted: ‎2024-11-08 08:06 AM
Hi @Rendi.ardian ,
Let's try to keep same IEC61850 Edition 1 in the protection relay to be more compatible with Sicam tool, on that P3 relay configuration you are working with Ed.2. Also please follow instructions I already explained previusly and disable also from "Optional Fields" the "Entry ID" option. Then, extract the .cid file and try to upload again on Sicam Pas. It should work.