Protection & Control
Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.
Link copied. Please paste this link to share this article on your social media post.
Happy to share the launch letter of the Easergy P3's FW 30.206. Take your time to through the attached announcement.
The FW is in production already. Easergy Pro ver 4.2.0 is required for this FW . Release date for EP will be 10 Nov 2022.
Link copied. Please paste this link to share this article on your social media post.
The 5th harmonic was added in FW30.205-1 already:
FW30.205.1 release functionality
This release contains the following up-dates for the P3T32, P3M32 and P3G32 requested by regions.
• SW selectable phase CT secondary current between 1 A or 5 A. This applies to such hardware which has
5 A phase current inputs in Slot 8. They are
o E = 3L(5A) + 2Io(5/1A+1/0,2A) + 4U
o 1 = 3L(5A) + 2Io (5/1A+1/0,2A) ringlug + 4U
• Up graded and restored 5th harmonic blocking stage for the dI> stage.
• Added START signals for 87dI>, 87dI>>, 64REF dIo> and 64REF dIo>> stages. They are visible in matrix,
DNP3, IEC101, IEC103 and IEC 61850 protocols.
• Added TRIP signals of 64REF dIo> and 64REF dIo>> to IEC 103 communication protocol
Link copied. Please paste this link to share this article on your social media post.
Hi Pekka.
I have a question regarding the 5th harmonic blocking, which was removed in function 87. Will they be included again?
Link copied. Please paste this link to share this article on your social media post.
The 5th harmonic was added in FW30.205-1 already:
FW30.205.1 release functionality
This release contains the following up-dates for the P3T32, P3M32 and P3G32 requested by regions.
• SW selectable phase CT secondary current between 1 A or 5 A. This applies to such hardware which has
5 A phase current inputs in Slot 8. They are
o E = 3L(5A) + 2Io(5/1A+1/0,2A) + 4U
o 1 = 3L(5A) + 2Io (5/1A+1/0,2A) ringlug + 4U
• Up graded and restored 5th harmonic blocking stage for the dI> stage.
• Added START signals for 87dI>, 87dI>>, 64REF dIo> and 64REF dIo>> stages. They are visible in matrix,
DNP3, IEC101, IEC103 and IEC 61850 protocols.
• Added TRIP signals of 64REF dIo> and 64REF dIo>> to IEC 103 communication protocol
Link copied. Please paste this link to share this article on your social media post.
Dear Experts,
Hope all are doing great.
Can you send me the link to download Easergy P3 FW 30.206 ?.
Thanks & BR,
Ardhanari
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Where can I find the FW30.206 file?
Link copied. Please paste this link to share this article on your social media post.
You mean the FW? if yes then here: 07. Firmware and Translation Files
Link copied. Please paste this link to share this article on your social media post.
I don't have access to schnider sharepoint. Can you send me the latest firmware for P3U30 attached in email?
Link copied. Please paste this link to share this article on your social media post.
Hi Mr.PekkaHAMALAINEN,
This is Gogulnath Manoharan from Saudi Arabia. We used the P3U30 & P3U20 relays in our project. We are facing issue that relays were not auto rebooting after changing the configuration. we have facing this issue in several relays. Is this issue will resolve if we updrade the firmware from V30.203 to 30.206. please share your openion to resolve this issue. If you provide firmware upgrade procedure and file will be better. My email id is mgogulnath@sepco.net.cn
Link copied. Please paste this link to share this article on your social media post.
Hi Mr.PekkaHAMALAINEN, i have a problem with authorization in microsoft (AADSTS90072: User account 'a.gyske@gmail.com' from identity provider 'live.com' does not exist in tenant 'Schneider Electric' and cannot access the application '00000003-0000-0ff1-ce00-000000000000'(Office 365 SharePoint Online) in that tenant. The account needs to be added as an external user in the tenant first. Sign out and sign in again with a different Azure Active Directory user account), please send the version FW30.206 to the mailbox: a.gyske@gmail.com