Greetings,
I have a P3F30 relay and I can access its configuration via front panel USB Type-B connector using Easergy Pro. My relay is ordered with a VSE002 RS485 connector and it does not have any Ethernet RJ45 connector. I can read values using MODBUS from SCADA but I cannot access its configuration remotely via Easergy Pro.
Is it possible to access the relay configuration via the serial connector at the back (VSE002) ??
Regards.
Link copied. Please paste this link to share this article on your social media post.
Any updates on this ??
Link copied. Please paste this link to share this article on your social media post.
Hello Sir,
As far as I understood, VSE002 is an interface used to connect VIO 12 I/O module (twisted pair interface to VIO) to P3F30 (Standard). You will not be able to connect on a P3x relay using Easergy_Pro through this module.
See table enclosed
BR
Thiago Carreiras