Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Configuring HUe as a 61850 Server

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Configuring HUe as a 61850 Server
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Araceli_Monje Mentor
60
Arun-kumar_PS
Arun-kumar_PS Mentor
26
JuanRayo
JuanRayo Mentor
24
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
Windsor
Windsor Mentor
Mentor

Posted: ‎2020-12-02 10:17 AM . Last Modified: ‎2023-05-30 10:13 PM

0 Likes
1
1110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-12-02 10:17 AM

Configuring HUe as a 61850 Server

I am trying to create a configuration for an HUe RTU that will act as a 61850 server. and will eventually communicate with a PowerSCADA Operation system. The RTU will have local acquisition modules and will also communicate to downstream IEDs using Modbus TCP/IP.

 

I have configured the 61850 server node in Easergy Builder with logical nodes, datasets and report control blocks so that local acquisition data can be published upstream, but I'm not sure what I need to add in order to support the monitoring and control of the downstream IEDs.

 

Any advice will be greatly appreciated.

Labels
  • Labels:
  • Application cases
  • Saitel range
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TomBerry
TomBerry Troubleshooter
Troubleshooter

Posted: ‎2020-12-02 12:19 PM

1 Like
0
1106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-12-02 12:19 PM

The general steps are :-

- Use the Easergy Builder IEC 61850 plugin, ICD editor to create a new ICD with the Logical Nodes to hold the data for each type of Modbus device.


- In the IEC61850 plugin, use the new ICD to create a new Logical Device (and NOT a physical device)  This updates the SCL but not the variables.

 

- In Easergy Builder, create the remote Modbus device(s) and create their variables as usual
-- For status and analogs, set the source addresses for Modbus, and the i61 bin controller as the destination.
-- For commands, the i61 bin controller is the source and the Modbus device is the destination

 

- Set up / extend the report control blocks and datasets for data from the Logical Device(s).
(I find CET850 is much easier to use for this than Easergy Builder)

 

If the remote device is a Schneider product, please let me know.
I may be able to find a suitable ICD, and/or I have an experimental Excel tool that generates an ICD file from a list of variables. 

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Reply 1
TomBerry
TomBerry Troubleshooter
Troubleshooter

Posted: ‎2020-12-02 12:19 PM

1 Like
0
1107
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-12-02 12:19 PM

The general steps are :-

- Use the Easergy Builder IEC 61850 plugin, ICD editor to create a new ICD with the Logical Nodes to hold the data for each type of Modbus device.


- In the IEC61850 plugin, use the new ICD to create a new Logical Device (and NOT a physical device)  This updates the SCL but not the variables.

 

- In Easergy Builder, create the remote Modbus device(s) and create their variables as usual
-- For status and analogs, set the source addresses for Modbus, and the i61 bin controller as the destination.
-- For commands, the i61 bin controller is the source and the Modbus device is the destination

 

- Set up / extend the report control blocks and datasets for data from the Logical Device(s).
(I find CET850 is much easier to use for this than Easergy Builder)

 

If the remote device is a Schneider product, please let me know.
I may be able to find a suitable ICD, and/or I have an experimental Excel tool that generates an ICD file from a list of variables. 

 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore