I have measured the impedance at the connector of several circuit breakers that were on a damaged
powerlink bus, most of which have a common measurement of 22 to 25 ohms. And 2 of them have a measurement
of 46 ohms and 75 ohms. I already installed the bus with the breakers that have the common measurement and
they worked correctly. Is there a problem that connects the 2 that measure differently?
Link copied. Please paste this link to share this article on your social media post.
Dear Sir.
This product does not belong to the Protection & Control portfolio and therefore is not managed by this forum. The product belongs to our Home & Distribution Line of Business. Offer Manager of this product is Mr. Avinash Chaudhary (email details shared below). He may be able to support you with this topic.
Best Regards,
Araceli Monje.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Dear Sir.
This product does not belong to the Protection & Control portfolio and therefore is not managed by this forum. The product belongs to our Home & Distribution Line of Business. Offer Manager of this product is Mr. Avinash Chaudhary (email details shared below). He may be able to support you with this topic.
Best Regards,
Araceli Monje.