Application case with P3M30+RTD Module VIO 12AD with MODBUS TCP protocol (RSTP)
Protection & Control
  • EcoStruxure Power & Grid
  • Protection & Control
  • Application case with P3M30+RTD Module VIO 12AD with MODBUS TCP protocol (RSTP)
Araceli_Monje
Commander Araceli_Monje Commander
43
Arun-kumar_PS
Commander Arun-kumar_PS Commander
21
PowerLogic
PowerLogic P2
Back to Protection & Control
faisalamir
Lieutenant faisalamir Lieutenant
Lieutenant
Posted: ‎2021-10-06 06:12 PM . Last Modified: ‎2023-05-23 07:34 AM
1526
Dear colleagues,
Kindly need your valuable advice with the issue that I am facing now related application note
I have a motor feeder application using P3M30. These IED relay need to be interfacing with the existing SCADA through Modbus TCP protocol and using network protocol RSTP. The Relay also need to monitor RTD temperature using VIO 12AD module
I had configured the cortex number for this relay with the below selection:
Option card I is select for "K-RS232: and Communication interface is select for "N-2XRJ (Ethernet RJ-45 100Mbs, RSTP)
My question is: Whether is it possible to use option card I: "K" to communicate with VIO 12AD module by using VX082 (REL52825) cable?
Your kindly advice will be helpful
Thank you
Faisal Amir Siregar
  • Thumbnail of PowerLogic P2
    PowerLogic
    PowerLogic P2
View products (1)
  • Application cases
PekkaHAMALAINEN
Lieutenant PekkaHAMALAINEN Lieutenant
Lieutenant
Posted: ‎2021-10-06 11:01 PM
1
1524
VX082 is a cable used to connect VIO 12 to P3Ux (Standard).
For P3M30
- Select K = RS232 in slot 6
- Select VX067 (REL52823) cable. The other end of this cable shall go to VSE001 (optical interface with VIO) or VSE002 (twisted pair interface to VIO)
See table enclosed
Pekka Hämäläinen
PowerLogic P3
PekkaHAMALAINEN
Lieutenant
1
1525
For P3M30
See table enclosed
Pekka Hämäläinen
PowerLogic P3
faisalamir
Lieutenant
Posted: ‎2021-10-06 11:13 PM
Thank you @PekkaHAMALAINEN for this useful info