Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

PowerLogic P5, P7: ATS with MV CB (alternative with MV LBS: PowerLogic T300)

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • PowerLogic P5, P7: ATS with MV CB (alternative with MV LBS: PowerLogic T300)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
23
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
13
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
sesa211247_brid
Lieutenant sesa211247_brid Lieutenant
Lieutenant

Posted: ‎2024-05-03 07:29 AM . Last Modified: ‎2025-05-26 12:28 AM

0 Likes
8
1468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-03 07:29 AM

PowerLogic P5, P7: ATS with MV CB (alternative with MV LBS: PowerLogic T300)

Dear Expert community 

 

is there any plan to develop an ATS (Automatic Transfert Switch)  or ABT (Automatic Bus Transfert) Application  similar to the one sold by NR PCS-9651

https://www.nrec.com/en/web/upload/2019/05/08/15572827837172kuwwm.pdf 

 

they are a lot of opportunities in the Oil and Gas segment that require a such device 

 

this could be done on the Powerlogic P5 (P5T32) or P7 platform

 

if a such product is developed it will save a lot of time, money, efforts and reduce risks .

 

Hope this will be done 

 

Attachments
Labels
  • Labels:
  • Application cases
  • IEC61850
  • PowerLogic P5
  • PowerLogic P7
  • PowerLogic T300
Tags (4)
  • Tags:
  • english
  • P5 ATS
  • P7 ATS
  • T300 ATS
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa211247_brid
Lieutenant sesa211247_brid Lieutenant
Lieutenant

Posted: ‎2024-05-10 04:35 AM

0 Likes
0
1309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-10 04:35 AM

Thank You @Jinlei_Xing 

See Answer In Context

Reply
Replies 8
Jinlei_Xing
Commander Jinlei_Xing Commander
Commander

Posted: ‎2024-05-07 10:56 PM

1 Like
3
1375
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-07 10:56 PM

It's a good idea to have dedicated device for both ATS and High Speed Transfer, such as ABB SUE3000 and Siemens 7VU68. It is possible to develop such a device based on the existing P7 platform.

 Currently we have one product Micom P84H which is for High Speed Transfer, but this product is only for Chinese marking.

 

BR,

Jinlei XING

 

 

BR,

Jinlei XING

Reply
sesa211247_brid
Lieutenant sesa211247_brid Lieutenant
Lieutenant

Posted: ‎2024-05-09 01:02 AM

0 Likes
2
1352
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-09 01:02 AM

Thank You for your feedback @Jinlei_Xing 

could you share some document on the Micom P84H please (datasheet and user manual) ?

Thank you 

Reply
Jinlei_Xing
Commander Jinlei_Xing Commander
Commander

Posted: ‎2024-05-09 01:17 AM

1 Like
1
1346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-09 01:17 AM

The related P84H slides are attached. 

 

BR,

Jinlei XING

Attachments
Reply
sesa211247_brid
Lieutenant sesa211247_brid Lieutenant
Lieutenant

Posted: ‎2024-05-10 04:35 AM

0 Likes
0
1310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-10 04:35 AM

Thank You @Jinlei_Xing 

Reply
Stefan_Scharf
Ensign Stefan_Scharf Ensign
Ensign

Posted: ‎2024-08-16 12:10 AM

0 Likes
0
1089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-16 12:10 AM

The ATS function is planned in a later wave for P7 as a dedicated application function block, probably with wave 4 but it can be achieved already using the Fast scheme logic (FSL) & matrix together with a sufficent number of CT/VT inputs.

Reply
DMayberry
DMayberry Cadet
Cadet

Posted: ‎2024-08-19 07:00 AM

1 Like
1
1066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-19 07:00 AM

In the US,  Digital Power has developed these Auto Throw-Over (ATO) applications for the P5 using the imbedded IsaGraf logic engine.  These applications are being used for MV gear standard ATO systems (MM, MTM, MG, MTG) as well as the foundation for Digital Power's more complex solutions.

 

Reply
sesa211247_brid
Lieutenant sesa211247_brid Lieutenant
Lieutenant

Posted: ‎2025-02-20 12:47 PM

1 Like
0
594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-20 12:47 PM

Hello, any update about this application?

could you share the documentation and settings files ?

Reply
TomBerry
Lieutenant JG TomBerry Lieutenant JG
Lieutenant JG

Posted: ‎2025-02-21 07:55 AM

1 Like
0
563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-21 07:55 AM

The T300 HU250 module has a built-in ATS function intended for distribution network operation

With SC150 modules, this can operate switches within 300ms of voltage loss.

It is feasible to create a different configuration that communicates with protection relays instead.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of