Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-09 03:57 AM
Is it possible to get indication of the operating Lever when it is in place?
I believe it moves the contact S1?
But the problem is can it be easily taken outside the motor unit or does it need some extra wiring?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-10 02:26 AM . Last Modified: 2025-07-10 11:10 PM
Hello @Arttu ,
All indicator contacts are available on the Customer Junction Block available on the PCB.
S1 is not directly available and not related to Operating Lever presence. It seems not possible to have Operating Lever presence indication on RM6 (only mechanical interlocking).
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-09 04:22 AM
Hi @Arttu ,
Check if you have this kind of connector on the top of your cubicle motor.
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-09 04:32 AM
But thats from SM6, in RM6 it is close to that but not quite the same.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-10 12:15 AM . Last Modified: 2025-07-10 12:21 AM
Hello @Arttu ,
I have no picture of RM6, but this is similar.
You need to remove the top cover of the RM6 and the Terminal Block mounted on a PCBA will be available.
Please refer to the RM6 operation manual for more information.
Check also this document:
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-10 01:58 AM
How is this a solution to my original question?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-10 02:26 AM . Last Modified: 2025-07-10 11:10 PM
Hello @Arttu ,
All indicator contacts are available on the Customer Junction Block available on the PCB.
S1 is not directly available and not related to Operating Lever presence. It seems not possible to have Operating Lever presence indication on RM6 (only mechanical interlocking).
Regards,
Link copied. Please paste this link to share this article on your social media post.