Emergency panel back feed with a single 120V source with SPD

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Emergency panel back feed with a single 120V source with SPD
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
Bobakman
Crewman Bobakman
Crewman

Posted: ‎2025-06-17 07:38 PM . Last Modified: ‎2025-06-18 06:11 AM

0 Likes
3
122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-17 07:38 PM . Last Modified: ‎2025-06-18 06:11 AM

Emergency panel back feed with a single 120V source with SPD

In an emergency if power a  panel board  so that both 120V busses are powered by a single 120V generator source (Generator is an inverter type with only 120V, 240V is not available) will it damage any SPD's in the panel (All 240V breakers will be open in such a case so no 240V equipment will be powered)? Specifically I am concerned about a model 

QO2175SB Surge Q model since it does not have a two pole breaker for isolation being hard wired to the panel it will be connected to both busses powered only by one 120V source.
Please see generator wiring diagram attached.

Attachments
Labels
  • Labels:
  • How to
  • Knowledge
  • Safety - Electrical Fire Prevention
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Manon_Chaboud
Commander Manon_Chaboud Commander
Commander

Posted: ‎2025-07-10 02:02 AM

0 Likes
0
14
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-10 02:02 AM

Hello @Bobakman, 

Thank you for your question regarding the use of a single 120V inverter-type generator to backfeed both 120V busses in a panel that includes a QO2175SB Surge Protective Device (SPD).

 

In this setup, where both panel busses are energized from the same 120V source and all 240V breakers are open, there is a potential concern with the SPD. The QO2175SB is designed to operate across a standard 120/240V split-phase system, where it expects a 240V differential between the two hot legs. When both busses are fed from the same 120V leg, there is no voltage difference between them. This can lead to abnormal operating conditions for the SPD, which may result in reduced protection performance or even damage to the device over time.

 

Additionally, since the SPD is hardwired and not connected through a two-pole breaker, it remains continuously connected across both busses. This means it will still be exposed to whatever voltage conditions exist between those busses, even if they are not ideal for its intended operation.

While your approach of opening all 240V breakers is a good safety measure to protect connected equipment, it does not address the SPD’s exposure. In some cases, it may be more appropriate to use an SPD designed specifically for 120V single-phase systems when operating under these conditions.

 

Have a good day!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 3
S-W
Commander S-W Commander
Commander

Posted: ‎2025-06-23 11:51 PM

0 Likes
1
96
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-23 11:51 PM

Hello @Bobakman, thank you for your post, we'll come back to you!

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Bobakman
Crewman Bobakman
Crewman

Posted: ‎2025-06-24 07:35 AM

In response to S-W
0 Likes
0
85
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-24 07:35 AM

Thank you I look forward to a reply.
Bob

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Manon_Chaboud
Commander Manon_Chaboud Commander
Commander

Posted: ‎2025-07-10 02:02 AM

0 Likes
0
15
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-10 02:02 AM

Hello @Bobakman, 

Thank you for your question regarding the use of a single 120V inverter-type generator to backfeed both 120V busses in a panel that includes a QO2175SB Surge Protective Device (SPD).

 

In this setup, where both panel busses are energized from the same 120V source and all 240V breakers are open, there is a potential concern with the SPD. The QO2175SB is designed to operate across a standard 120/240V split-phase system, where it expects a 240V differential between the two hot legs. When both busses are fed from the same 120V leg, there is no voltage difference between them. This can lead to abnormal operating conditions for the SPD, which may result in reduced protection performance or even damage to the device over time.

 

Additionally, since the SPD is hardwired and not connected through a two-pole breaker, it remains continuously connected across both busses. This means it will still be exposed to whatever voltage conditions exist between those busses, even if they are not ideal for its intended operation.

While your approach of opening all 240V breakers is a good safety measure to protect connected equipment, it does not address the SPD’s exposure. In some cases, it may be more appropriate to use an SPD designed specifically for 120V single-phase systems when operating under these conditions.

 

Have a good day!

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of