Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-17 07:38 PM . Last Modified: 2025-06-18 06:11 AM
In an emergency if power a panel board so that both 120V busses are powered by a single 120V generator source (Generator is an inverter type with only 120V, 240V is not available) will it damage any SPD's in the panel (All 240V breakers will be open in such a case so no 240V equipment will be powered)? Specifically I am concerned about a model
QO2175SB Surge Q model since it does not have a two pole breaker for isolation being hard wired to the panel it will be connected to both busses powered only by one 120V source.
Please see generator wiring diagram attached.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-10 02:02 AM
Hello @Bobakman,
Thank you for your question regarding the use of a single 120V inverter-type generator to backfeed both 120V busses in a panel that includes a QO2175SB Surge Protective Device (SPD).
In this setup, where both panel busses are energized from the same 120V source and all 240V breakers are open, there is a potential concern with the SPD. The QO2175SB is designed to operate across a standard 120/240V split-phase system, where it expects a 240V differential between the two hot legs. When both busses are fed from the same 120V leg, there is no voltage difference between them. This can lead to abnormal operating conditions for the SPD, which may result in reduced protection performance or even damage to the device over time.
Additionally, since the SPD is hardwired and not connected through a two-pole breaker, it remains continuously connected across both busses. This means it will still be exposed to whatever voltage conditions exist between those busses, even if they are not ideal for its intended operation.
While your approach of opening all 240V breakers is a good safety measure to protect connected equipment, it does not address the SPD’s exposure. In some cases, it may be more appropriate to use an SPD designed specifically for 120V single-phase systems when operating under these conditions.
Have a good day!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-24 07:35 AM
Thank you I look forward to a reply.
Bob
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-10 02:02 AM
Hello @Bobakman,
Thank you for your question regarding the use of a single 120V inverter-type generator to backfeed both 120V busses in a panel that includes a QO2175SB Surge Protective Device (SPD).
In this setup, where both panel busses are energized from the same 120V source and all 240V breakers are open, there is a potential concern with the SPD. The QO2175SB is designed to operate across a standard 120/240V split-phase system, where it expects a 240V differential between the two hot legs. When both busses are fed from the same 120V leg, there is no voltage difference between them. This can lead to abnormal operating conditions for the SPD, which may result in reduced protection performance or even damage to the device over time.
Additionally, since the SPD is hardwired and not connected through a two-pole breaker, it remains continuously connected across both busses. This means it will still be exposed to whatever voltage conditions exist between those busses, even if they are not ideal for its intended operation.
While your approach of opening all 240V breakers is a good safety measure to protect connected equipment, it does not address the SPD’s exposure. In some cases, it may be more appropriate to use an SPD designed specifically for 120V single-phase systems when operating under these conditions.
Have a good day!
Link copied. Please paste this link to share this article on your social media post.