minimum levels of short-circuit NSX100H
Dear,
Displaying the curve for the NSX100H I see a minimum value in the magnetic protection of 239 A. It really means that it will trigger at 239A t<10ms or it is a precision treshold?
- Labels:
-
Power Distribution Software
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-29 02:09 AM
Hello
In general, the time-current characteristics curve has two boundaries.
The lower and upper boundaries.
The probability of the tripping would be as follows.
- The tipping will be sure to happen at the “zone above the upper boundary.”
- The tripping will not happen at the “zone blow the lower boundary.”
Regards,
Team – Ecodial Expert Support.
- Tags:
- ecodial
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-29 02:09 AM
Hello
In general, the time-current characteristics curve has two boundaries.
The lower and upper boundaries.
The probability of the tripping would be as follows.
- The tipping will be sure to happen at the “zone above the upper boundary.”
- The tripping will not happen at the “zone blow the lower boundary.”
Regards,
Team – Ecodial Expert Support.