>630A MCCB with 90C cables without derating.

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • >630A MCCB with 90C cables without derating.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
dhrobertson
Crewman dhrobertson
Crewman

Posted: ‎2024-06-05 02:00 AM

0 Likes
4
968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-05 02:00 AM

>630A MCCB with 90C cables without derating.

I am advised that NS800 MCCB can be handle 90C directly without derating. Please confirm.

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2024-06-13 07:28 AM

0 Likes
1
890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-13 07:28 AM

hello @dhrobertson 

Reference temperature for a Compact NS is 40°C (inside equipment), you can use 90°C Cable like 75°C cable, it don't change anythink,  You should to respect this derating table as advise. and you must to confirm the temperature respect on diferent points ( connection, frotn face , handle) in conformity with IEC 61439 internationnal standard

 

Capture d’écran 2024-06-13 162409.jpg

Best regards

 

 

Gregoire Brun
Breaker Product Expert

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
dhrobertson
Crewman dhrobertson
Crewman

Posted: ‎2024-06-12 10:55 PM

1 Like
0
912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-12 10:55 PM

No comments! extraordinary!

Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2024-06-13 07:28 AM

0 Likes
1
891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-13 07:28 AM

hello @dhrobertson 

Reference temperature for a Compact NS is 40°C (inside equipment), you can use 90°C Cable like 75°C cable, it don't change anythink,  You should to respect this derating table as advise. and you must to confirm the temperature respect on diferent points ( connection, frotn face , handle) in conformity with IEC 61439 internationnal standard

 

Capture d’écran 2024-06-13 162409.jpg

Best regards

 

 

Gregoire Brun
Breaker Product Expert
Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

dhrobertson
Crewman dhrobertson
Crewman

Posted: ‎2024-06-13 10:33 PM

In response to Gregoire_Brun
0 Likes
0
877
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-13 10:33 PM

Thank you M. Brun! In this case we have an NS800 with Ir = 0.8 x 800= 640A connected to bus bars on the input side and 1.5m of copper bus bars on the output side connected to a single set of 400mm2 XLPE cables. There are 34 sets of these installed. The enclosure is from 4B, ventilated, and the entire pod is cooled by CRAC to 25-28C. I understand the 75C max rating but will run a full load test and carry out a thermographic analysis. Your response and the tables provided are much appreciated!

Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2024-06-13 11:47 PM

0 Likes
0
867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-13 11:47 PM

 with pleasure @dhrobertson 

take tyime to check this 2nd table

Capture d’écran 2024-06-14 083555.jpg

 

For 640A section of 400mm² looks a little low, please check internal temp inside your equipment. 

 

When we check temp on breaker in accordance with IEC 60-947-2, we use 500mm² sections at 800A and 400mm² at 630A.

Best regards

 

Gregoire Brun
Breaker Product Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of