Power Distribution and Digital Support
Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-17 02:36 AM
Dear Sir,
We are programing and commissioning 2 Active Harmonic filter PCS+ having these reference: PCSP120D51P54 and PCSP300D51IP54.
supply source are generators and Solar through Inverters.
There is no public network grid.
Could you please advise if these AHF can work with generators and Solar inverters?
and if yes, Is there any condition to be ensured for generators and Solar inverters specifications so they can be connected to AHF ?
when we start and run the AHF we got message : "AC line not qualified "
we see that frequency of generator and solar is 52/53 Hz .
we tried to set the Frequency in AHF manually but we are not able to select other than 50 or 60 HZ .
Is it allowed and possible to set for example 51 or 52 to be within the range (+- 3 Hz ) so the AHF does not stop ?
thanks and awaiting your feedback
Regards
Charbel
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-17 01:16 AM
Hello!
AccuSine should allow to use frequency of 50Hz +/-3Hz. The issue might be on different levels (see attachment).
Link to the user manual: AccuSine+_User-Manual.book (schneider-electric.com)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-17 01:16 AM
Hello!
AccuSine should allow to use frequency of 50Hz +/-3Hz. The issue might be on different levels (see attachment).
Link to the user manual: AccuSine+_User-Manual.book (schneider-electric.com)
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.