are mccb trip units required

Power Distribution and Digital

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Solved
blaggy
Cadet
0 Likes
4
415

are mccb trip units required

Hi

 

i want to use a 250A nsx mccb for distribution. Am i right in thinking the trip units are only needed for adjustable requirements?

 

thanks


Accepted Solutions
RHH-Eltechna
Commander | EcoXpert Master Commander | EcoXpert Master
Commander | EcoXpert Master

Re: are mccb trip units required

Hello @blaggy ,

 

You are correct to say that with a micrologic you have way more input on the trip of the circuitbreaker.

The thing is there is also a difference in kind of protection.

With Micrologic you have electrical protection while when you use a TM-D for instance its only Thermal-Magnetic protection.
It totally depends on what you want to use it for. 


I found this little extra info online for you to get it a bit more understandable;
note: short circuit protection needs quick trip than
overload trip thats why thermal trip is used for Overload
Protection And Magnetic Property is used for shortcircuit
Protection.

In Microprocessor release, sensing and triping executed by
Micrprocessor in gives the very faster response than TMD
Release. Normally Microprocessor based release gives LSI
Protection

 

Hope this gives you a bit more insight.


Kind regards,

Rick - Eltechna B.V.
signature-RHHH

See Answer In Context

Tags (1)
J_Travostino
Admiral Admiral
Admiral

Re: are mccb trip units required

Hello @blaggy ,

 

Considering Trip Units can be electronic (Micrologic) or Thermal Magnetic (TMD), they are anyway always necessary into circuit breakers.

Basically, they ensure protection again short circuits and overheating. 

If you don't have a trip unit, your circuit breaker main function (protecting humans and goods) is not achieved. 

 

 

Julien Travostino
Power Distribution & Digital forum community owner
Power Products Div.

See Answer In Context

Tags (1)
HelvinHermanT
Captain Captain
Captain

Re: are mccb trip units required

Hi, 

 

If you use MCCB without Trip unit, then it will have fuction as Switch only to manualy ON & OFF. It will not trip unless you manually turn it ON or OFF.

 

Some application use MCCB as Manual Switch for Isolation purpose only (Not Protection purpose), so no need Trip unit.

 

But as other expert mentioned, if you need MCCB to work as protection such as Overload Protection and Short Circuit Protection, then you must use trip unit too.

See Answer In Context

Tags (1)
4 Replies 4
RHH-Eltechna
Commander | EcoXpert Master Commander | EcoXpert Master
Commander | EcoXpert Master

Re: are mccb trip units required

Hello @blaggy ,

 

You are correct to say that with a micrologic you have way more input on the trip of the circuitbreaker.

The thing is there is also a difference in kind of protection.

With Micrologic you have electrical protection while when you use a TM-D for instance its only Thermal-Magnetic protection.
It totally depends on what you want to use it for. 


I found this little extra info online for you to get it a bit more understandable;
note: short circuit protection needs quick trip than
overload trip thats why thermal trip is used for Overload
Protection And Magnetic Property is used for shortcircuit
Protection.

In Microprocessor release, sensing and triping executed by
Micrprocessor in gives the very faster response than TMD
Release. Normally Microprocessor based release gives LSI
Protection

 

Hope this gives you a bit more insight.


Kind regards,

Rick - Eltechna B.V.
signature-RHHH
Tags (1)
J_Travostino
Admiral Admiral
Admiral

Re: are mccb trip units required

Hello @blaggy ,

 

Considering Trip Units can be electronic (Micrologic) or Thermal Magnetic (TMD), they are anyway always necessary into circuit breakers.

Basically, they ensure protection again short circuits and overheating. 

If you don't have a trip unit, your circuit breaker main function (protecting humans and goods) is not achieved. 

 

 

Julien Travostino
Power Distribution & Digital forum community owner
Power Products Div.
Tags (1)
HelvinHermanT
Captain Captain
Captain

Re: are mccb trip units required

Hi, 

 

If you use MCCB without Trip unit, then it will have fuction as Switch only to manualy ON & OFF. It will not trip unless you manually turn it ON or OFF.

 

Some application use MCCB as Manual Switch for Isolation purpose only (Not Protection purpose), so no need Trip unit.

 

But as other expert mentioned, if you need MCCB to work as protection such as Overload Protection and Short Circuit Protection, then you must use trip unit too.

Tags (1)
J_Travostino
Admiral Admiral
Admiral
0 Likes
0
285

Re: are mccb trip units required

Hello @HelvinHermanT ,

 

Totally agree with you. 

To complement it: even if you need a Switch disconnector, you must have a "Trip unit-style" block as shown below (red circled).

It has not protection function but is mandatory to be assemblied.

Capture.JPG

 @blaggy ,

For more information about Switch-disconnectors MCCBs: ComPacT NSX NA, check out this link 👈

 

 

Julien Travostino
Power Distribution & Digital forum community owner
Power Products Div.
Tags (1)